Discuss Test PC setup. in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

E

entech

Hi chaps , been testing some pc set ups. Each station has a pc supplied with a standard 3 pin iec , and a monitor with a standard 3 pin iec.

Been testing the cords separate for earth continuity, insulation and polarity. Then i connect cords and then test again, pc for earth bond at 100mA, insulation at 250 then touch test, then monitor tft for insulation,then touch test. (cant get good earth bond as majority plastic)..

So in all four tests per station.

Would you carry out the same tests or more/less???

Cheers
 
Hi entech, I would do similar to you, but I would not carry out a Touch Current test after a successful Insulation test on the PC or monitor.
The Touch Current test is often referred to as a substitute soft test, because it is usually used when an insulation test cannot be performed or gives suspect results. Because the Touch Current test is a powered test it should always be preceded by an Insulation test.
There is nothing wrong in doing the Touch Current test in addition to an Insulation test, but you may save yourself time and two tests per PC system.
When you are testing in a commercial or industrial setting with hundreds or thousands of items, every minute saved is valuable, particularly if the job is priced piece-rate.
 
Last edited by a moderator:

Reply to Test PC setup. in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Looking for some guidance here. I'm currently shadowing a guy and we're testing a new extension on a school. 3 phase TNCS supply from the original...
Replies
6
Views
2K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
I have just been out for a pre works visit to fit an electric shower. I cant access the CU as it has a cupboard built in the way. It's a TT and...
Replies
40
Views
6K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock