Discuss Test Results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
hpmuk
Hi All
Quick questions on test results
With Continuity tests i know R1 + R2 results depends on the length of run & size of cable..
When testing it cant be more than a certain figure depending on cable size and breaker size.
How would i know the maximum readings should be? Im guessing on site guide but couldn't find it?
If this is correct do we know a page??
Cheers in advance
Luke
pp 100 - 104 red osg. a blind monkey could have found that in less than a minute.
Your maximum permitted R1&R2 would theoretically be the maximum permitted Zs of the circuit, minus the external earth fault loop impedance.
So, R1&R2 = Zs - Ze.
However these give you a worst case scenario approach which will not be accurate.
Alternatively, you can obtain the design information to establish the circuit length, then you could more accuraely calculate the expected measured R1&R2 values.
Hi All
Cheers in advance
Luke
Student? If yes Then please state this when asking questions. we do not do students homework on this forum !
Advice if genuine however is free, and if we have given advice do feel free to hit the THANKS button
OK, Luke, we are looking to have an EFLI low enough to trip the circuit's MCB/fuse within the BS7671 specified time. ( generally 0.4 secs. for circuits up to 32A.)
this EFLI ( max, ) is found in tables in the bgb, with temperature corrected figures in osg. ( the theory behind this is basically ohms law. the lower the impedance, the larger the fault current. the larger the current, the quicker the MCB/fuse will break ). this figure is Zs. which is composed of Ze + (R1+R2). Zeis obtained either by enquiry or measurement, then when you take that from Zs, you get a max. value for your R1+R2.
Reply to Test Results in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...