If it is SELV CT-E remember to test for continuity from centre-tap to earth, and ensure it is earthed when you IR test the primary to earth, in order to prove the insulation of the windings as well as the circuit.
As far as I know you test the primary side as submains and then has 2 circuits each at 55v to Earth . 16A fuse testing each line.
wheres the neutral Lol
Ps is there anyway of knowing what overloads are set at on a vsd
(RLV) isn't SELV