Hi just a quick question. I've seen a few times people say test insulation resistance 250v first to make sure there isn't any points missed in loft or where ever. This seem to me a sensible thing to do. Is it 100% safe to test all ways l-n l-e n-e. I thought it was as its not far of the running voltage but someone at work today disagreed.
You could still zap some very sensitive electronic equipment with 250V DC from a megger, you'd be pretty unlucky but it can happen, I always try it on the kOhms setting first, If you can't be sure use test method 2 and note it on your paperwork.
Nothing wrong with testing at 250v as a precaution before testing at 500v. If you dont test at 500v you are not testing it properly, the reason it is 500v is to put the cable under a bit of pressure.
You could connect L and N together and test them to E, this way you wont do any harm, but if you do a lighting circuit you will still need to remove dimmers as they are in the line only, and you will damage them.
If you are new to testing, then you are doing the right thing by asking, but i advise all who post similar questions to go and buy IET Guidance note 3, this is the testing bible, and is very easy to understand, and is priceless in you position.
Cheers............Howard
Reply to Testing at 250v in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...