Discuss Testing in the UK Electrical Forum area at ElectriciansForums.net
L1Jay1
On a continuity test on existing lighting circuit, do all bulbs have to be removed, what if there is to many or some can’t be reached.
Trainee Electrician
you don't remove for a continuity test. but without removing all loads, you can't do a L-N IR test.
no you don't need to remove. you are measuring either R2 or R1+R2. as the bulbs are connected L-N, their resistance will have no effect on your readings.
its just that in college, they said lamps should be remved for R1 R2 test
Perhaps they are teaching you how to conduct the series of tests for an installation, not just continuity. In that case, all loads would need to be removed first.
Yeah you’re right, the tests done in college are for a new installation, looks like with a existing lighting circuit, the lamps don’t need removing .
During initial verification, r1+r2 or r2 needs to be confirmed at the furthest point. The only way to measure r1+r2 or r2 is physically removing the lamp/cover and gain access to the conductors.
If you are performing r1+r2 this is a good time to confirm polarity too using the light switch.
Actually, during initial verification cpc continuity must be verified at all points.
Have you got an RCD warning label to read?
If not, look it up in the regs. or on line, even.
I was asking if the RCDs are switched to the off position during insulation resistance test, as I know they are sensitive equipment.
[automerge]1577561827[/automerge]
On IR test can u just switch RCDs off or do u actually have to dis them.
Disconnect them it was meant to say
[automerge]1577562141[/automerge]
Sorry disconnect them , my post was meant to say.
I believe you are correct. I thought it was Zs that had to be proved at every point but yes, I believe it is continuity of cpc at every point.
A Zs wouldn't confirm a cpc is present or that it is a acceptable condition or terminated sufficiently
You can't carry out Zs until the installation is energised, and you can't safely energise an installation without proving the correct connection of the protective conductor at every point.
This is why the continuity of the protective conductor is tested first.
Yes exactly. Hence why I realised my mistaken thoughts
Reply to Testing in the UK Electrical Forum area at ElectriciansForums.net
Hi All DALI lighting system distributes circuit via LCM's, for electrical test, do you stop at the LCM or light point. how do you carry out...
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hi, looking for some ideas on this. I went to an address on Tuesday following a storm where property has been struck by lightning. When the...
I got a TEXT message (i dont know them and i cant find out who they are from the phone number) "Hi speaking from Indeed Are you available to give...