Hi 2 all,a ring main is installed in a roof space of a bungalow using 2.5 t/e,protected by a 32amp rcbo,the cable laid on top of existing insulation,years later,we r all goin green,the thickness of the insulation exceeds 100mm,how does this effect the final ring circuit calculations etc.If installing a 2.5 radial in the same conditions ref method101 the cable is derated to 17 amps,so is that the case of a ring main circuit,ie;32 amps now rated at 17amps,& protected by a 16 amp rcbo & not a 32 rcbo cheers hav a nice day,ta ra bab
 
Are you saying, that you have 100mm of new insulation laid on top of the existing insulation and thus surrounding the ring main cables in insulation??

If so, then yes you will need to apply the appropriate de-rating factor. Unless of course you can bring the ring main cables to sit on top of the insulation, as they were originally. Then as they are not surrounded in insulation, no de-rating will apply.
 
i wonder how many existin properties r left with that scenario,& how many consultants never ever take termal insulation into consideration,how many ring main circuits hav u seen on a 16 amp rcbo,i hav never put a ring on less than 32 amps.The insulation surounds all the cable,
 
People installing loft insultion have little or no respect, or knowledge probably, for the impact they are having on electrical installations
 
Sorry Im a bit late jumping in on this topic but does anyone know what the calculation to size the ring main protective device is? Eg the Iz of 2.5 installed to method 101 is 17 amps what is the maximum mcb size?
I'm guessing its Iz x1.6 which give 27 amps so a 20 or 25 mcb would be fine.

Help please ive been looking for this for ages.
 
From the above posts I am no longer sure but I would say that for 2.5mm T&E cable installed to method 101 (T&E cable clipped to a wooden joist and covered by >100mm insulation) the current carrying capacity of the cable is 17A, since you have a RFC there are two cables each taking half the current so CCC of the circuit is 34A maximum size protective device is 32A assuming no other rating factors apply.
 
Hi Rich, thanks for trying to help. I ended up speaking with my NICEIC area engineer so I asked him for some advise. He said 433.1.103 (new green book) tells us for a 32a ring each conductor Iz must be a minimum of 20a. So to work out the minimum IZ for a 20a ring you would calculate

20/32= 0.625

20x 0.625 = 12.5a

So a 20a ring main would therefore need each cable to have a minimum Iz of 12.5a (perfect for install method 103).

To go back to the original scenario with cables installed to method 101, a RFC in 2.5mm t+e could be installed on a 25a mcb.

Sorry to answer my own question but I thought it might be useful to someone else like me who has to design circuits for well insulated buildings.
 
Last edited by a moderator:

Reply to thermal insulation in the Australia area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
730
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hi We recently had an 7kW EV charger installed. Due to the consumer unit being situation within the kitchen of our bungalow, the cable needed to...
Replies
10
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock