Yes, that's what I said, the black and grey should be sleeved brown if they are on the same phase as the brown, if they are on different phases they shoukd not be sleeved brown.
You misunderstood me.
If the three phases are being used to supply single phase equipment, for instance 3 lighting circuits each on a different phase, then the conductors should be sleeved brown (or otherwise identified as being line conductors).
 
That’s probably a scenario where checking the phase rotation would be a good idea.
How long did it take before you asked a Rock Ape to sort out the socket wiring?
It's Phase Sequence Lads not Rotation, from Pete999 the Pedant.:tongue::tongue:
 
You misunderstood me.
If the three phases are being used to supply single phase equipment, for instance 3 lighting circuits each on a different phase, then the conductors should be sleeved brown (or otherwise identified as being line conductors).

For 3 single phase circuits like that you'd use brown for each live, you wouldn't install black and grey. Or if it's in a multicore cable then you wouldnt have a black and grey as it would be at least a 7core which will have all cores the same colour.
 
There is a requirement to ensure correct phase rotation throughout an Installation in Chapter 6.
I think it’s a bit pointless, as when you connect 3 phase machinery, if it runs backwards, you just swap one of the phases over.
Some machines don't like being run backwards. Best to get it right first time.

Why would you need 7 core?
5 core would do, share the neutral between the 3 phases.
Then it would be one 3-phase circuit, but you were talking about three single-phase circuits:
for instance 3 lighting circuits each on a different phase,
Each of which will have a line and a neutral.

There are two aspects to the OP. One is getting the sequence right, which three out of the six possible permutations will be. As far as machine rotation is concerned, L1, L2, L3 and L3, L1, L2 are equally good. But if you don't know which phase is which, single-phase loads can't be connected to a known phase which is sometimes desirable, e.g to even out known load imbalances.
 
Some machines don't like being run backwards. Best to get it right first time.
Now how would you do that?
How would you ensure that the new machine required the same phase rotation as that in your installation?

As far as I’m concerned, the only time ensuring phase rotation is the same throughout an installation would be beneficial, is if you intend moving a machine to various locations around an installation.

Also, most 3phase machines use L1 to supply control circuitry, so swapping phases around in an installation would help balance out loads.
Instead of all the control circuits being on L1, they would be spread accross all the phases.
 
Now how would you do that?
How would you ensure that the new machine required the same phase rotation as that in your installation?

As far as I’m concerned, the only time ensuring phase rotation is the same throughout an installation would be beneficial, is if you intend moving a machine to various locations around an installation.

Also, most 3phase machines use L1 to supply control circuitry, so swapping phases around in an installation would help balance out loads.
Instead of all the control circuits being on L1, they would be spread accross all the phases.
By machine I assume you mean 4 phase motors? if you have had any electrical work in your place of work, and you fear the phase sequence is not the same as it was, then I would suggest you uncouple the mechanical elements run the motor without any load to check you have the correct phase sequence for this particular motor, once you have checked and swapped phases at the motor, reconnect the mechanicals and off you go, as for taking the control from L1 surely it matters not which phase the control supply comes from.
 
How would you ensure that the new machine required the same phase rotation as that in your installation?
The majority do seem to like L1, L2, L3 or R, S, T.

In a factory environment where a board is only supplying 3-phase loads, each of which has three anonymous brown cables in an isolator or busbar tapoff, it's not particularly interesting to know which phase is which. You can test the sequence at the machine terminals before starting it up. But if you have a mixed load, where single-phase circuits might even dominate the total load at times and certainly overshadow the single-phase control loading of 3-phase machines, it's helpful to be able to balance them.

In the entertainment industry we use a lot of 3-phase supplies for mainly single-phase loads but with some 3-phase loads mixed in. I might plug a hoist control box into any one of a dozen 3-phase outlets in a venue. If I swap out some of the hoists, I don't want them to be overrunning their limits because they are wired the other way. At the same time, if I know there's a total of 160A to play with spread amongst three 125A circuits, I need to know that loading L1 to 100A in one DB and L2 to 100A in another DB is not going to catch me out mid-show because they are actually on the same supply phase.

I agree that it's not always essential to know which phase is which, but it's not terribly difficult to organise.
 
The majority do seem to like L1, L2, L3 or R, S, T.

In a factory environment where a board is only supplying 3-phase loads, each of which has three anonymous brown cables in an isolator or busbar tapoff, it's not particularly interesting to know which phase is which. You can test the sequence at the machine terminals before starting it up. But if you have a mixed load, where single-phase circuits might even dominate the total load at times and certainly overshadow the single-phase control loading of 3-phase machines, it's helpful to be able to balance them.

In the entertainment industry we use a lot of 3-phase supplies for mainly single-phase loads but with some 3-phase loads mixed in. I might plug a hoist control box into any one of a dozen 3-phase outlets in a venue. If I swap out some of the hoists, I don't want them to be overrunning their limits because they are wired the other way. At the same time, if I know there's a total of 160A to play with spread amongst three 125A circuits, I need to know that loading L1 to 100A in one DB and L2 to 100A in another DB is not going to catch me out mid-show because they are actually on the same supply phase.

I agree that it's not always essential to know which phase is which, but it's not terribly difficult to organise.
Good call Lucien, I was overthinking things, of course if you have the equipment, you could, as you say check and confirm phase sequence with a meter, what was I thinking of?????? Dohhhhh
 
Yes you can do that at the machine.
But what’s the point in ensuring phase rotation is consistent throughout an installation?

You have an installation where phase rotation has been checked throughout.
You install a new machine, it runs backwards.
You swap the phases round in the machine, it runs forwards.

You have an installation where phase rotation has not been checked throughout.
You install a new machine, it runs backwards.
You swap the phase round in the machine, it runs forwards.

What’s the difference?
When I was in the RAF we had a hangar with 6 separate bays where we moved 3 phase machines with 125A plugs around depending on aircraft requirements. Bay 2 (I can even picture it right now) was wired the wrong way round meaning that every time a machine went in or out of there one of us had to swap the phases round. Our contractors were like you and couldn’t see the problem. Hours of work over years due to incompetence on the part of the original inspector that signed it off.
The majority do seem to like L1, L2, L3 or R, S, T.

In a factory environment where a board is only supplying 3-phase loads, each of which has three anonymous brown cables in an isolator or busbar tapoff, it's not particularly interesting to know which phase is which. You can test the sequence at the machine terminals before starting it up. But if you have a mixed load, where single-phase circuits might even dominate the total load at times and certainly overshadow the single-phase control loading of 3-phase machines, it's helpful to be able to balance them.

In the entertainment industry we use a lot of 3-phase supplies for mainly single-phase loads but with some 3-phase loads mixed in. I might plug a hoist control box into any one of a dozen 3-phase outlets in a venue. If I swap out some of the hoists, I don't want them to be overrunning their limits because they are wired the other way. At the same time, if I know there's a total of 160A to play with spread amongst three 125A circuits, I need to know that loading L1 to 100A in one DB and L2 to 100A in another DB is not going to catch me out mid-show because they are actually on the same supply phase.

I agree that it's not always essential to know which phase is which, but it's not terribly difficult to organise.
in my current role I work on wind turbine lifts which come with phase rotation relays. This prevents the lift operating in the event of incorrect phase connections.

Of course the original installer in the factory has got to connect the phase relay up the right way round in the first place. I had to go to one a couple of weeks back that rather disconcertingly for the client was trying to drive itself through the floor when they pushed the up button.
 
Now how would you do that?
How would you ensure that the new machine required the same phase rotation as that in your installation?

As far as I’m concerned, the only time ensuring phase rotation is the same throughout an installation would be beneficial, is if you intend moving a machine to various locations around an installation.

Also, most 3phase machines use L1 to supply control circuitry, so swapping phases around in an installation would help balance out loads.
Instead of all the control circuits being on L1, they would be spread accross all the phases.

Machines that would come to harm or would impact safety due to the rotation will have phase rotation relays on them locking it down.

Or they should have...
 
Now how would you do that?
How would you ensure that the new machine required the same phase rotation as that in your installation?

As far as I’m concerned, the only time ensuring phase rotation is the same throughout an installation would be beneficial, is if you intend moving a machine to various locations around an installation.

Also, most 3phase machines use L1 to supply control circuitry, so swapping phases around in an installation would help balance out loads.
Instead of all the control circuits being on L1, they would be spread accross all the phases.

Machines that would come to harm or would impact safety due to the rotation will have phase rotation relays on them locking it down.

Or they should have...
 
My experience is varied.
Had machines that run backwards and need phases swapped.
Had replacement motors that run backwards and need phases swapped.
Had re-wound motors that run backwards and need phases swapped.
Had one machine with a number of motors, that have required some of the motors to haves phases swapped.
Had two supplies to one installation where the phases are not in sync.
In this instance, the second supply was for a smoke extract system.
Normal supply, the fans extracted. Emergency supply, the fans blew.
 

Reply to Three phases main supply in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
591
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
842
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
448
Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
839
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Replies
1
Views
436

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock