Hello, I have a 12VDC battery bus where I charge with solar PV and a wind turbine. The system is controlled using a Siemens PLC. When there is a system fault, the PLC will open all relays, but this included relays that power the PLC itself (example an emergency pushbutton). When restarting the system (Black start), I need a way to temporarily connect the batter bus to the Inverter that powers the PLC. the current upon start up I believe will be as high as 30A, so I am looking for a solution that will allow about 50A to pass for about 5mons, and then automatically switch it self off. I am currently achieving this using a manual breaker, but the risk is someone forgets to switch off the breaker. Can anyone recommend a time delay switch that can work here (max 150VDC, 50Amps)? I am trying google but not really getting anywhere. I suspect there are existing electrical systems that have a similar black start requiement.
 
https://www.albrightinternational.com/product_family/low-voltage-stud/

Push-Button Switches | Rapid Online - https://www.rapidonline.com/Push-Button-Switches

The first link is to a maker supplier of heavy duty dc contactors. I leave it to you to select a suitable SPST device with appropriate coil voltage.

I assume '5 mons' is 5 minutes. This timer-relay can be set to provide a 5 minutes on pulse after receiving a control pulse from a normally open push button:

RS PRO Off Pulse, ON Pulse with Control Switch, ON Pulse without Control Switch, On-Off Pulse Multi Function Time Delay | RS Components - https://uk.rs-online.com/web/p/timer-relays/1617612/

This timer-relay (see above) will repeat the sequence every time the control push button is pressed.

If you do not want that to happen once the PLC has powered up then you will have to arrange for this circuitry (ie the push, timer-relay and dc contactor) to be inhibited until another shut-down has occurred. This could be done by another simple relay sensing the state of the system (viz operational or shut down/fault - an output from the PLC or inverter?) whose NC contacts are used in the inhibition role I mentioned earlier - in series with the dc supply to the contactor coil and push button for example. Or we could look at another timer-relay which has a one-shot mode.

If you want I will look over what you propose as a solution.
 
Last edited:
A couple of observations,

The PLC is loosing power when there is a fault.
What's the cause of the fault(s) and how often are they?
It might be simpler to overcome the faults than to have to keep restarting (regularly?)

Second, it seems unusual that the PLC is powered from the circuit(s) it controls.
Is this a standard system supplied by a manufacturer or a one off put together just for this system?

Are there any circuit diagrams for it?

Additional thought, this must be off grid and the only 240ac is from the inverter?
If so maybe the PLC needs it's own control cct inverter.
 
Last edited:
If the PLC can turn the inverter off, surely it already has a power contactor or logic control input, and the black start override only needs to operate that, not carry the whole inverter current?

And yes, it would seem better to power the PLC separately so that ordinary fault scenarios don't shut it down.
 
ShaneA: it would be nice to see a sketch/pictures/diagram of the system 'to tickle our fancy' and understand better your problem. Perhaps you might elaborate?

:)

Marconi
 

Reply to TIme Delay Switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
971
DYI guy here with some basic knowledge of electrical craft. I am helping a buddy in his remodeled bathroom. His GFCI outlet was powered off vanity...
Replies
11
Views
955
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
888
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi guys, I don’t really know where to post this, sorry if it’s in the wrong place. After posting a thread about old lead sheathed cable in my...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock