sparks1653

i have just been to carry out a site visit for a possible project. the house has an 80A TNS supply. there is a studio built in the garden that has just been wired, there are mistakes everywhere...for example main supply is 2.5mm cable supplying a 63a board.... the list continues. anyway the owner said the electrician also fitted an earth spike which i didnt expect as the ZE from the studio was way to high. after fitting an earth spike he recorded a reading of 25.8 ohms on the minor works cert. my knowledge of TT is limited as i dont really ever deal with it in london. should i remove the spike all together as im going to replace the cable to the studio anyway so could run a higher CSA earth cable as well to then be connected to the MET, what are the resistance reading regs for TT? i will start by taking a Ze measurement from the main house which i didnt get a chance to do today
 
Get the house converted to PME for a start, then see the sticky thread on 'Exporting PME to Outbuildings'. Factors like whether the outbuilding has gas/water supplied, i.e. extraneous conductive parts, will determine what you can do.

Any TT Ze over 200ohms needs to be investigated as it could be unstable. Its all in the OSG and Big Red (Green now) Book sparks 1653.
 
Get the house converted to PME for a start, then see the sticky thread on 'Exporting PME to Outbuildings'. Factors like whether the outbuilding has gas/water supplied, i.e. extraneous conductive parts, will determine what you can do.

Are you for real?? convert a TN-S for PME?? Think you should read the OP post again, you got lost somewhere along the way!!!
 

Reply to TNS/TT combined in the Australia area at ElectriciansForums.net

Similar Threads

Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Replies
5
Views
1K
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
1K
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Need some advice, I have 7 static caravans to connect which need to be connected via TT 1. All the vans have a 30ma RCD main switch internally...
Replies
6
Views
897
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock