I can't remember whether the qu mentioned if 0.23 was the measured live conductors resistance (ie R1+RN). I myself, didn't use any correction factors, but can see why people have. I thought the that 1.2 correction factor was for correcting the R1+R2 part of the Zs=Ze+(R1+R2) equation, as its carried out as a dead test, and therefore the conductors aren't at operating temperature? But thinking about it... The same logic could be applied to an R1+RN test?

It mentioned that it was the total measured resistance of R1 and Rn and that the testing was done at an ambient temp of 20 deg C.
 
Looks like the correction factor is needed! This was from the previous chief examiners report on c and g website...

"When asked to calculate the voltage drop for a given scenario most candidates failed to include a temperature compensation factor in their calculation. As testing was carried out at 20 oC and voltage drop is calculated with the conductors at operating temperature this compensation needs to be included in the calculation."

damn it! I didn't use any correction factor, so don't know if I'll have picked up any points for that, or the question that followed on from it asking if it complied or not? I but it complied, which it would've with or without the correction factor, as both were <11.5 volts

- - - Updated - - -

I put*
 

Attachments

  • image.jpg
    212.1 KB · Views: 33
well, spark_shark you had me thinking i had done the right thing there. Until i remember'd that for reasons unknown to me my correction factor was something like:-

40x0.23=9.2v correction factor of 1.2 required, but i thimk i have done 1 / 1.2, wich then lowers the bloody voltage to 7.6v!!!!!!!!!!!!!!!!
when it should have gone up to 11.04v!!!!!!!!!!
were i got 1 divided by 1.2 from?????????????? put it down to resit nerves!
 

Reply to Today's 2395 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi Guys, I'm looking at booking myself on the 2391. Just wanted to see if anyone has ever done the course online and then done the 2 day exam. If...
Replies
5
Views
665
Could anyone point me to somewhere online I can go through some fault coding photo examples for 2391 52? I've passed everything else, just have to...
Replies
1
Views
3K
Hi all Is anyone aware of the change to solar generation FIT payment contracts for existing installations. (FIT payment scheme closed in 2019)...
Replies
8
Views
852
Hi I'm trying to get some closure on an on-going issue I have in regards to a final qualification certificate which is the C&G 2360 Part 2. I...
Replies
6
Views
2K
Hello sparkly people Im a total beginner around how electricity really works. Ive recently been made redundant from ground works in construction...
Replies
2
Views
731

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock