Call out this morning guy saying there was a strong smell of fish coming from the cupboard where his CU was. Trying not to laugh down the phone, I asked him a couple of question and then forced myself to go to investigate for myself.

Turned up and right away strong smell of "fish".

Small single BS3871 CU unitadjacent to the main CU where the smell is really coming from. Its feeding the shower on a 30A breaker 6mm T+E. Check it out and see that part of the plastic has began to melt. Open it up and see that the T+E cable CPC is badly burnt and the sleeving is toast. The CPC coming from the supply end is a 4mm single core going straight to the Henley block where the main earth is. TNC-S system.

Disconnect everything and check the shower switch and the shower itself. Find that an old friend who is now a retired electrician, had connected up the shower and had connected the N and CPC round the wrong way.

Anyways, swaped round, reconnected everything, quick couple of tests to check all in order. Happy days.

My question is, this was done 4 years ago according to the customer, shower does look that old. Anyone any clues as to why it took that long for the fault to develop? Really couldn't get my head around it. Said they use the shower everyone morning for the three of them. Sure this should of started causing problems right away or well before now?

Was also told that last month they had a friend who is an electrician out swapping their oven over who noticed they had no main earth from the cut out to their main CU. He threw in a 16mm cable for this to sort that problem.
 
Call out this morning guy saying there was a strong smell of fish coming from the cupboard where his CU was. Trying not to laugh down the phone, I asked him a couple of question and then forced myself to go to investigate for myself.

Turned up and right away strong smell of "fish".

Small single BS3871 CU unitadjacent to the main CU where the smell is really coming from. Its feeding the shower on a 30A breaker 6mm T+E. Check it out and see that part of the plastic has began to melt. Open it up and see that the T+E cable CPC is badly burnt and the sleeving is toast. The CPC coming from the supply end is a 4mm single core going straight to the Henley block where the main earth is. TNC-S system.

Disconnect everything and check the shower switch and the shower itself. Find that an old friend who is now a retired electrician, had connected up the shower and had connected the N and CPC round the wrong way.

Anyways, swaped round, reconnected everything, quick couple of tests to check all in order. Happy days.

My question is, this was done 4 years ago according to the customer, shower does look that old. Anyone any clues as to why it took that long for the fault to develop? Really couldn't get my head around it. Said they use the shower everyone morning for the three of them. Sure this should of started causing problems right away or well before now?

Was also told that last month they had a friend who is an electrician out swapping their oven over who noticed they had no main earth from the cut out to their main CU. He threw in a 16mm cable for this to sort that problem.


Maybe the Fault was always there, but took a long time to cause the burning, bit fishy that.
 
  • Like
Reactions: 1 person
When the bloke did the new 16mm earth a month or so ago to the main CU did he disturb the 4mm earth [neutral] to the shower CU I wonder ?
 
Perhaps a full condition report is in order, just in case any other friends have been around........ :)
 
Anyone any clues as to why it took that long for the fault to develop?

Connections to heavily loaded / slightly overloaded cables that are not very tight do tend to slowly develop high resistance and eventually fail catastrophically. All terminals with reasonable load on experience thermal cycling, as the cable heats the terminal up things expand and tighten, but loosen again as they cool down. If they are not tight enough to remain completely gas-tight thoughout, air can penetrate the contact surfaces and gradually oxidise them, leading to higher resistance, more heat, more oxidation. It can take years for this to really set in but once the contact surface starts to corrode badly it can arc and get very hot very quickly.
 
  • Like
Reactions: 7 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Today's callout
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Thread Tags

Advert

Thread statistics

Created
StevieTee,
Last reply from
Lucien Nunes,
Replies
4
Views
1,239

Advert