If the circuit is all ok and test confirm circuit is not faulty you could try the circuit for a short time on an MCB , then once elements have warmed up replace MCB with the RCBo again , worth a try that is of course if the RCBo is not faulty and tests out alright , disconnect circuit completely to carry out the RCD test though..
 
Looks like some electricians on this thread have no concept of what an induction hob is!. It is basically a high power low frequency radio transmitter connected to a coil under each pan location. The pan is heated by eddy currents induced in the pan. Note that such a hob will have a large number of RF filters including caps L to E and N to E. These caps will cause a large amount of leakage current and also provide a good path for any RF noise from elsewhere to earth. I would suggest first clamp it to find out the level of earth leakage and then fit a good RCD that also has transient suppression.
 
Hi guys

Interested in your thoughts here. I recently installed a new circuit to supply an induction hob and oven. The circuit is supplied via a 40 amp rcbo. The rcbo however is intermittently tripping, sometimes when it's not even in use and stone cold I.e no fan etc running. I know the loading is correct and this is not an overload fault.

I'm thinking it's a faulty oven unit/hob unit - it's brand new and straight out the box.

Or do induction hobs require a type c breaker to cope with the inductive load
- if that's how they work? Iv fitted induction hobs before in type b breakers and never had a problem.

Any thoughts?

Thanks.
Dan
Gasp !!!
 

Reply to tripping induction hob in the Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
822
We have an install where the client has supplied an induction/gas hob combination unit. We have a 6mm cable supplying the hob, the induction part...
Replies
3
Views
960
Hello All. I'm quite new to this game and gaining experience, but going well in the main. My customer wants to feed a Hob ( on island in centre...
Replies
5
Views
243
Hi all, I've just tried wiring an indesit IB65B60 induction hob. I read the instruction manual and it said for 240v connections to put the...
Replies
23
Views
4K
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock