I changed a couple of sockets at a property I am working on and put my plug tester in to check and it tripped the rcd. Tried a couple of times then took sockets off to check them - all ok. Tried to do loop test with my kew 63 tester - tripped again. Tried a few other sockets in property and all tripped out. Plugged Dyson into same sockets and it worked fine. Consumer unit is 30 year old split load unit with 100mA rcd main switch and 30mA secondary rcd. Can test ok on 100mA rcd side but trips on testing secondary side. Connections ok inside. Has anyone come across this type of fault before. I seem to recall it happening before on another consumer unit which I changed. I believe it was an MK unit as is the one I am writing about now.
 
Puzzled as to why there's a 100mA RCD on one side of the board and a 30mA on the other - what's the supply type? Or do you actually mean a 100A main switch, not an RCD??
 
Puzzled as to why there's a 100mA RCD on one side of the board and a 30mA on the other - what's the supply type? Or do you actually mean a 100A main switch, not an RCD??
there is 100A rcd main switch ( TT system ) with lighting circuits on that rail and a 2nd rail with 30mA rcd on it powering sockets. I cannot do any tests on 30mA rcd side because it trips as soon as I plug in my socket tester or kew 63 meter. It is 30 years old and I am changing it. I am fairly confident that the rcd is faulty - there is no other possibility. Thanks for the input.
 

Reply to Tripping Query in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
808
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
321
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock