Hi GC,Hi,
I have recently had a hot tub fitted and am not comfortable with it being supplied directly from TN-C-S supply. I’m looking for someone to modify to TT, but struggling to find anyone locally who can help.
Location - Warrington, Cheshire.
Thanks.
Hi,
I have recently had a hot tub fitted and am not comfortable with it being supplied directly from TN-C-S supply. I’m looking for someone to modify to TT, but struggling to find anyone locally who can help.
Location - Warrington, Cheshire.
Thanks.
Hi GC,
Could you explain your worries a little more?
It's unusual for a customer to even know what TNCS is, you clearly do and you are worried about it. Did you discuss it with the electrician before hand?
I haven't checked the most up to date regs on this, but did find the following from an (older) NICEIC article...
"Hot Tubs and TN-C-S Supplies The NICEIC Technical Helpline is often asked whether a hot tub installed outdoors may be supplied from a circuit taken from an installation forming part of a TN-C-S system, often referred to as a PME Supply. Neither the Electricity Safety, Quality and Continuity Regulations nor the guidance given in Engineering Recommendation G12/4 – Requirements for the Application of Protective Multiple Earthing to Low Voltage Networks published by the Energy Networks Association places any restrictions in respect of the connection of a hot tub to a PME supply. G12/4 does offer several alternatives in respect of the connection of a swimming pool to a PME supply and it is sometimes suggested, erroneously, that hot tubs should be treated in the same manner as a swimming pool. However, it is clear that hot tubs fall outside of the scope of Section 702 of BS 7671 (see Regulation 702.11). So, unless, as stated previously in this article, a hot tub outdoors is installed within the zones of a swimming pool, only the general rules of that standard are applicable."
But the chance of a fault on a PME system is about chance of getting a kiss from a garaff.
Appreciate the comments so far.Hi,
I have recently had a hot tub fitted and am not comfortable with it being supplied directly from TN-C-S supply. I’m looking for someone to modify to TT, but struggling to find anyone locally who can help.
Location - Warrington, Cheshire.
Thanks.
I am not in your area so too far for me (North Yorkshire), as for advice without seeing the site any advice on-line would have to be rather generic. But I can see you want a discussion so will quickly start this off.Appreciate the comments so far.
Anyone in the North West able to help, or at least advise on this?
Thanks.
Thanks for the response, makes perfect sense.I am not in your area so too far for me (North Yorkshire), as for advice without seeing the site any advice on-line would have to be rather generic. But I can see you want a discussion so will quickly start this off.
One of the issues (there are many to be considered) you have with hot tubs outdoors is the possible clash between manufacturers instructions and BS 7671 in particular BS 7671 411.3.1.1 which states:
(quote) 'Simultaneously accesible exposed-conductive parts shall be connected to the same earthing system...' (end quote)
Now this is not always as simple as it might suggest yet for want of any other information I offer it as the first question to be addressed. Hot Tub manufacturers may well state TT yet acceiving such in an area with TN-C-S is not that straight forward.
Yet it is possible and as this is what you the customer requires the design now needs to be looked at to see how this can be achieved. Now I am not saying it can be achieved for any one set of circumstances a site survey would be required and perhaps to assist somewhat photographs of the hot tub area, location from the main house and any out-buildings would assist
I have certainly heard of (some) Electricians unwilling to enter into discussion on matters of this form so what you say rings true. It is not for me to guess why for it seems a reasonable technical issue that a customer is faced with and skilled competent people can engage with. I wish you well with your search, there will be someone willing to come along, drink a coffee and discuss this through with you - Disclaimer: more cost may be incurred than just a spoonful of coffee at the survey stage.
I have carried out such works but it requires a good deal of 'spade work' before deciding to go ahead.
Any advice without being on-site must be taken as generic and may not be the best option for your circumstances. Some of the considerations however, for / against etc I am happy to bat around in a civil way
I am not in your area so too far for me (North Yorkshire), as for advice without seeing the site any advice on-line would have to be rather generic. But I can see you want a discussion so will quickly start this off.
One of the issues (there are many to be considered) you have with hot tubs outdoors is the possible clash between manufacturers instructions and BS 7671 in particular BS 7671 411.3.1.1 which states:
(quote) 'Simultaneously accesible exposed-conductive parts shall be connected to the same earthing system...' (end quote)
Now this is not always as simple as it might suggest yet for want of any other information I offer it as the first question to be addressed. Hot Tub manufacturers may well state TT yet acceiving such in an area with TN-C-S is not that straight forward.
Yet it is possible and as this is what you the customer requires the design now needs to be looked at to see how this can be achieved. Now I am not saying it can be achieved for any one set of circumstances a site survey would be required and perhaps to assist somewhat photographs of the hot tub area, location from the main house and any out-buildings would assist
I have certainly heard of (some) Electricians unwilling to enter into discussion on matters of this form so what you say rings true. It is not for me to guess why for it seems a reasonable technical issue that a customer is faced with and skilled competent people can engage with. I wish you well with your search, there will be someone willing to come along, drink a coffee and discuss this through with you - Disclaimer: more cost may be incurred than just a spoonful of coffee at the survey stage.
I have carried out such works but it requires a good deal of 'spade work' before deciding to go ahead.
Any advice without being on-site must be taken as generic and may not be the best option for your circumstances. Some of the considerations however, for / against etc I am happy to bat around in a civil way
Yes I can see you have a reasoned approach. All the best with the search.Thanks for the response, makes perfect sense.
When I say advice, I mean if anyone is local to us and can advise in person. I understand any advice on the forum will be generic and this situation is dependent on many things about the specific site/setup.
Does it seem reasonable to have two RCD/RCBO inline to prevent single point of failure in a TT ‘island’ setup? Is it OK for both of these devices to be upstream of the TT island (i.e. at consumer unit on supply earth, then switch to TT earth at the hot tub end)?Yes I can see you have a reasoned approach. All the best with the search.
only one should be put in ,two in series is no good .Does it seem reasonable to have two RCD/RCBO inline to prevent single point of failure in a TT ‘island’ setup? Is it OK for both of these devices to be upstream of the TT island (i.e. at consumer unit on supply earth, then switch to TT earth at the hot tub end)?
Unless it's time delayedonly one should be put in ,two in series is no good .
The concept is good yet - disclaimer - design would still be required to implement such.Does it seem reasonable to have two RCD/RCBO inline to prevent single point of failure in a TT ‘island’ setup? Is it OK for both of these devices to be upstream of the TT island (i.e. at consumer unit on supply earth, then switch to TT earth at the hot tub end)?
Apologies if my wording is flawed or if this is a nonsense concept!
Thanks.
To TT at the Hot Tub end, yes, I have done so myself and is often easier. Just ensure you have complete isolation between the two earthing systems at this point of separation (perhaps at the isolator) and any other sources. 'Insulation' tape is not considered a suitable insulation - despite the name it adopts.