We have came across an upgraded db, the installation about 20 years old, and this db change happened this year.

The db as not been bought up to 18th edition regulations and just been swapped like for like.

We are carrying out a EICR on this db, I understand the db should off had a EIC but this was from another company. Would you code 2 all the non compliance with the 18th edition? No rcd on sockets and no rcd on lights within shower area, remembering the installation 20 years old but just had a new db.

Thanks
 
The fact that the new work doesn't comply with the 18th Edition shouldn't affect how you code the observations - this is an assessment of the safety (or otherwise) of the installation. So once you've assessed the severity of the non-compliance then which Edition/Amendment of the Regulations was in force at the time really isn't relevant.
 
In my mind the whole point of the EICR coding is the danger, not if it matches current regulations or not.

I would follow the Best Practice Guide #4 for coding as it is a justifiable stance in all cases (so C2 for lack of RCD only if supplying outside sockets, etc).

EDIT: Just beaten by @Risteard !
 
The issue of the DB change not being to the current regs is really an issue for the client to address with the electricians who did the work.
 
Does it count as like for like replacement / maintenance?
Might not have needed a certificate at the time.
Who knows what modifications have been carried out on the installation in the previous 20years (compliant or otherwise).
A replacement DB always requires testing and an EIC in my book, and Part P notification.
Certainly not as simple as changing a 'like for like' light fitting!
Not sure I've ever done a 'like for like' db change as there is always (or seems to be) some upgrade!
 

Reply to Upgraded db regulations in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
511
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
379
In Theory that’s a good argument but if you will be adding or moving switches or sockets or adding lights you’ll more than likely end up needing a...
Replies
7
Views
474

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top