As per title, urgent advice needed.

I have an ELECSA assessment tomorrow for the installation work and condition reporting. I am fine with EICRwork to show, but the person with whom I agreed that her install by me will be checked tomorrow, called me at 3pm today that she will not going to be able to be at the property. I did other installs around my area but no one is available,too short notice. So it happens I have nothing to show. So I decided as thelast resort to change my old CU.


I just done all essential tests on my property before hand to make sure nothing stops me to do the work, everything seems fine, no barrowed neutrals, ring continuity with all 3 stages ok, IR ok, Ze just fine for TNCS being 0.33


I cannot start works now because I have tenants (helps pay mortgage)back from work and they need electricity, so basically I have just tomorrow early in the morning time to do it before 9.30am. I have all gear in place.


My concern is, meter tails needs upgrading to 25mm2 and the earthing conductor to 16mm2 and bonding to 10mm2, at the moment I have 16,10,6 respectively. Bonding to gas and earthing conductor comes out of the head where its splits from neutral, so I have no chances to do upgrades on those without puling the main fuse out, normally I should call DNO to disconnect the supply for me to do works, but I will not ge tthem to do it in time for me, is it?


So please can you advice what my options are, and how the assessor reacts in all that awkward situation.


Thanks in advance for any helpful advice given

Best regards. Al
 
Last edited:
leave tails in , just change main earth and bonding.
i'm sure if you look hard enough you'll notice the fuse seal is missing anyway.
;-)
 
Well they'll charge if you cancel as I tried last year as I was as sick as a dog... No joy, so I just was honest and said I'm very ill, but come take a look anyway.

You have nowt to lose, if you can show you can test, know the regs and can explain what you are going to do to finish the install, I'd say you will be fine, but you will need to forward pics of the work that is to be completed.
don't worry the assessor will use his judgment if you explain your situation.
 
Elecsa assessors do allow you to show them a job which is "work in progress" - so can you get your tenents out of the way for the morning?
 
Make sure you have all your paperwork, public liability insurance, mft calibration certs, in one place ready to show him/her.
show him the previous certs that you were going to use for the assessment. Double check your certs that you are filling put for you consumer unit change as they may well check your readings and ask questions on the result, a favourite in an electric shower, or immersion heater.

Ben
 
I think worst case scenario is that any non compliances will require photo evidence of rectification within 30 days. Easily solved, no more cost or visits.
Don't sweat it. Explain the situation to the guy, and I'm sure all will be cool.
 
They will be happy enough if you actually have the knowledge to know the tails and bonding need upgrading as its in progress. They will just want to see you test I wouldn't worry at all
 

Reply to urgent advice needed in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
539
Completed my AM2s start of this year. My whole career plan is to run my own company/sole trader. Be my own boss basically. I always get asked...
Replies
14
Views
702
Hi all, I completed my level 2 2365 installation and my level 3 8202 advanced technical diploma in electrical installation and I’m unsure on...
Replies
1
Views
774
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
607
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
439

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock