My boss has just took over a new site and I went to look the layout. Some boards are damaged some cables need replacing and am sure some other stuff. The site has a old busbar with isolators feed various boards and of her isolators. It also has a board connected directly on to the busbar . The main switch for this board is rated 125a the tails are 35mm ,but the fuse in the maintenance isolators are 250amp DD fuses. So the board and the tails have no protection. My question is (and I know it's late so be gentle) could I swap the main switch for a MCB , or will I have to relocate and feed it off a isolator with correct fuses (the board is a Hager tp and n Invicta3 ) . Now to go home and bed
 
Check out section 433 and 434 regarding placement of an OCPD at less than 3 meters Where there’s a change in the ccc of conductors and the following conditions it requires where overload and fault protection are placed on the load side.
 
Very common to have tails connected to a 250 amp busbar and then straight into an Isolator, I have seen 6mm2 tails connected to a 400 amp busbar before with the 32 amp Isolator bolted to it, very common practice years ago and you will see Busbars now still all over the country with the same set ups. In factories for example everything was bolted to a busbar and the tails from them to the busbar no where near the size of the incommer, no problem at all under this set up.
 
Very common to have tails connected to a 250 amp busbar and then straight into an Isolator, I have seen 6mm2 tails connected to a 400 amp busbar before with the 32 amp Isolator bolted to it, very common practice years ago and you will see Busbars now still all over the country with the same set ups. In factories for example everything was bolted to a busbar and the tails from them to the busbar no where near the size of the incommer, no problem at all under this set up.

It's still common practice among experienced electricians.

There are specific regs that allow this practice.
 
Unless I have read it incorrectly, the OP is saying the DB is fed direct from the busbar which feeds several circuits. So there is no overload protection for the tails feeding the DB.
 
Unless I have read it incorrectly, the OP is saying the DB is fed direct from the busbar which feeds several circuits. So there is no overload protection for the tails feeding the DB.

There is also a 250A fused isolator in there somewhere but I can't decipher if it before the busbar chamber or betwixt chamber and DB.
 
I’m reading it, that there are 3 x 250A fuses, then the bus bar and then the feed to the DB taken off the bus bar.
Regulations allow protective devices to be installed within 3m of where a reduction in CCC of a conductor occurs.
If the 250A fuses are correct for the bus bar and the tails between the bus bar and the DB are less than 3m, there’s no problem.
 
There is also a 250A fused isolator in there somewhere but I can't decipher if it before the busbar chamber or betwixt chamber and DB.
I think thats whats is protecting the cables feeding the bus if the OP has expressed concern, also 35mm tails feeding the DB
 
Yes the 250ampnduses are protecting the whole busbar other isolators are connected going off the. Feed other stuff (not important) but the board in question is bolted on to the busbar with no peotprotec . I could of course remove the board and fit a isolator and relocate the board (but am lazy).tha t is why am asking about the MCB for main switch. (sorry if the details in my post was confusing , just wanted to give as much detail as Possible
 
I’m reading it, that there are 3 x 250A fuses, then the bus bar and then the feed to the DB taken off the bus bar.
Regulations allow protective devices to be installed within 3m of where a reduction in CCC of a conductor occurs.
If the 250A fuses are correct for the bus bar and the tails between the bus bar and the DB are less than 3m, there’s no problem.

There is a problem if the DB has the potential to take the current through those 35mm tails over what they can handle and lower than the 250A fuses.

Op - there needs to be some sort of OCPD between the bus bar and the DB. You need to ensure those tails can not be overloaded and if I have read the op correctly those tails, in there current state could be overloaded long before the 250A fuses blow.
 
Yes the 250ampnduses are protecting the whole busbar other isolators are connected going off the. Feed other stuff (not important) but the board in question is bolted on to the busbar with no peotprotec . I could of course remove the board and fit a isolator and relocate the board (but am lazy).tha t is why am asking about the MCB for main switch. (sorry if the details in my post was confusing , just wanted to give as much detail as Possible

Are you talking about replacing the main switch with say a 63A MCB in the DB?
 
You say the DB is a Hager invicta 3. If it a 250A board you can get 125A and 250A MCCB incomers. If it's a 125A board they don't do MCCB incomers for them.
An alternative could be a switch fuse on top of the busbar next to the DB.
 
Yes the board has a 125 incoming kit I was thinking of use a 80a MCB if it will fit or if not move stuff around so I can use the isolator next to it loop a few feet of 35mm over into the top of it to feed it ,remove the current tail from the board and change the fuses to match .
 
Yes the board has a 125 incoming kit I was thinking of use a 80a MCB if it will fit or if not move stuff around so I can use the isolator next to it loop a few feet of 35mm over into the top of it to feed it ,remove the current tail from the board and change the fuses to match .

You can get 125A incomers for both the 125A and 250A boards, so it could be either. If it is a 250A board you will be able to get a MCCB incomer.
 
Ive had a similar issue before on an EICR..

200A fuses > into busbar chamber > 35mm tails mechanically protected for 2m into DB > db only rated at 125A, so not fusing down for the tails is fine as somebody else said i cant remember reg no., but theres nothing stopping you pulling in excess of 125A through the main switch....

My only options to remedy were to fit a 63A type C mcb.... Or leave it, the current install in question could never overload it so it was left as a C3.

note it had been inspected by quantec who advertise on here 5 yearly twice before i did it and they hadnt even picked it up.

I did buy the mcb though, still sits in my cupboard, its Havells so has probably gone up in value :D
 
Am I missing something here? If the 35mm singles are mechanically protected and under 3 meters then there is no requirement for an OCPD to be placed before the DB. Its not really no different to a 100A main fuse in a house with 16mm tails feeding a CU...As long as the load has been assessed, taking diversity into account that the CCC of the 16mm tails wont be exceeded. Or as in the OP the rating of the main switch in the DB. Or have I read the OP totally wrong?
 

Reply to Using a MCB as a main switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Has anyone fitted an SPD to a schneider standalone AFDD DB. Isobar P B Standalone Active distribution board, Acti9, 24 AFDD ways This board only...
Replies
4
Views
812
Good evening, I wondered how the MCB between RCD and the Main switch is wired while watching this video. Photo attached. I assume a busbar link is...
Replies
3
Views
849
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
633
Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock