I didn't think this could get so complicated, lol.
I'm using table 4E4A on page 348 of 7671. 16mm 2 core swa. Reference method E (the cable is being run on the surface) - It shows CCC of 115amps.
Then calculating the VD from table 4E4B 16mm 2 core single phase at 2.9mV.
I'm running from a TNC-S supply and have calculated a loop impedance of 1.1915 ohms.
I'm running 3 x twin sockets close to the board through individual 16amp breakers for which Table 41.3 allows a max. 2.87 ohms to meet the disconnection times.
I've admitted - many times - on this board, that I am primarily a domestic installer. But i do come here to get educated when I'm not 100% sure of the odd job which falls my way. But, I am having a problem understanding why I can't export the equipotential earthing out to this cable. I do so when I run to garden huts etc. and while this particular building is 170m away, I can't see there being a problem so long as I can match disconnection times. As for a fault with the DNO supply, wouldn't this effect the farmhouse, milking shed and out-buildings which are all drawn from the same supply?
Apologies in advance if I seem dumb, but I can't get my head around it.