Hi
just a quick q
when you have a single have supply and 2 consumer units supplied off Henley block and there is no double pole main switch between meter and Henley, Ie. isolation by each main switch in consumer units, are you required to place a warning label for multiple supplies.
I have a feeling you are but wanted to confirm with others.
cheers
 
I am not quite following what you say, but if you are saying what I think you are then there are not multiple supplies in the above. It is two boards supplied from one supply, tee'd off at the Henley. Same as a single board it would be isolated at the main switch with the incoming tails remaining live.
 
Multiple supplies labels refer to more than one supply i.e. PV and Generator supplies , as well as the normal supply In your case its one supply , Why Multiple ?
 
Hi guys,
thanks for the quick responses, yes the gay owl you are correct. 60 a single phase supply tails from service head to meter to Henley then two sets of tails to each consumer unit. Just had a thought on a job I was on yesterday and normally I see a double pole isolator between meter and Henley so thought that a label would be needed as there is no single point of supply/ isolation. Ie you would need to isolate each consumer units main switch. But it makes sense what you and R G have said, just me overthinking things. Thanks
APE
 
Last edited:
Just to expand that a little, that is for multiple supplies isn't it.

But with one supply as per the OP, there should be a main switch for the installation.

No for multiple supplies you need a label to identify this and all of the points of isolation.

I was talking about multiple main switches which requires that each main switch be clearly identified.

Unfortunately, although it goes against a lot of common sense, it is permitted to not have a single main switch, although personally I don't think it is good practice.
 
Same here davesparks, I think it is better practice to have one point of isolation as well. Which I think is what threw me as to need a label.
thanks to all for responding.
 
No for multiple supplies you need a label to identify this and all of the points of isolation.

I was talking about multiple main switches which requires that each main switch be clearly identified.

Unfortunately, although it goes against a lot of common sense, it is permitted to not have a single main switch, although personally I don't think it is good practice.
My interpretation of 537.1.4 is that there should be one point of isolation for the installation.

A main switch at the origin.

The double pole switches in the consumer unit are the main switch for that consumer unit but then there must be a main switch for the installation. As I interpret it.

What do you think?

Let me add this isn't an argument, just discussion.
 
Last edited:
My interpretation of 537.1.4 is that there should be one point of isolation for the installation.

A main switch at the origin.

The double pole switches in the consumer unit are the main switch for that consumer unit but then there must be a main switch for the installation. As I interpret it.

What do you think?

Let me add this isn't an argument, just discussion.

The way I read it is if there is one CU the CU main switch is good enough.

Split the tails then there should be an isolator prior to the split. - Not that may people do this as it adds costs!
 
Guidance note 2 says something along the lines of....A dwelling can have more than 1 electrical installation therefore one main switch is not required to isolate all consumer units simultaneously providing the consumer units have an integral main switch. Its a requirement that each device used for isolation to be clearly identified by positional or durable marking to indicate the installation it isolates. How ever the guidance notes are just that guidance and I agree its prudent to have a single point of isolation.
 
No for multiple supplies you need a label to identify this and all of the points of isolation.

I was talking about multiple main switches which requires that each main switch be clearly identified.

Unfortunately, although it goes against a lot of common sense, it is permitted to not have a single main switch, although personally I don't think it is good practice.
It's not permitted by the Regs.
 
Guidance note 2 says something along the lines of....A dwelling can have more than 1 electrical installation therefore one main switch is not required to isolate all consumer units simultaneously providing the consumer units have an integral main switch. Its a requirement that each device used for isolation to be clearly identified by positional or durable marking to indicate the installation it isolates. How ever the guidance notes are just that guidance and I agree its prudent to have a single point of isolation.
Yes it can have more than 1 installation.
However each installation would be connected to separate terminals at the meter, as would be the case with economy 7.
Splitting the tails however does not make two installations.
 
Last edited by a moderator:
Hi guys,
great info, just wondering if you went to a house and found this set up without a double pole main switch to isolate all and all you was doing was adding a new socket or maybe something a bit more involved like a new circuit, would you insist on installing one. It seems a bit too much if you are only doing a small job. I think if I was adding a new circuit or adding to an existing, I don't think I would insist but if I was changing a board or both boards I would. Just wondering what others think.
 
So as an example if i was asked to add a garage supply to an existing installation where the main consumer unit does not have sufficient ways i would have to......
A) ask the d.n.o to attend one day never to isolate the supply at the head.
B) Install a main switch in a metal enclosure after the meter before splitting the supply at the henley.
C) Charge the client again for another s/fuse unit to protect the supply to the garage.
D) Charge the client again for another board within the garage which also has another d/pole main switch within.

In total we have now put in 3 points of isolation for a garage!!
TBH i can't see the point of this switch between the meter and henley. Both boards have their own isolation. With a single board your isolator still does not isolate the supply upstream. Putting an isolator before the henley block still does not kill the supply upstream of it.
 
Would this single point of isolation not be more required where you have two completely separate supplies entering the same premises. This single point of isolation in this instance makes more sense.
 
So as an example if i was asked to add a garage supply to an existing installation where the main consumer unit does not have sufficient ways i would have to......
A) ask the d.n.o to attend one day never to isolate the supply at the head.
B) Install a main switch in a metal enclosure after the meter before splitting the supply at the henley.
C) Charge the client again for another s/fuse unit to protect the supply to the garage.
D) Charge the client again for another board within the garage which also has another d/pole main switch within.

In total we have now put in 3 points of isolation for a garage!!
TBH i can't see the point of this switch between the meter and henley. Both boards have their own isolation. With a single board your isolator still does not isolate the supply upstream. Putting an isolator before the henley block still does not kill the supply upstream of it.
Well when your adding the Henley blocks to split the tails you'd install a isolator before that. Your making it out to be a big thing. You've already got the supply off to split the tails haven't you?. So just add an isolator too.

For example It gives an ordinary person a quick and simple way of isolating the installation in an emergency etc.

I don't know why your mentioning the supply up stream, are you getting mixed up. IF there is one consumer unit then the main switch in that is fine, if 2 consumer units then there needs to be one point of isolation, as is the discussion. So an isolator would be fitted.
 
Last edited:
My interpretation of 537.1.4 is that there should be one point of isolation for the installation.

A main switch at the origin.

The double pole switches in the consumer unit are the main switch for that consumer unit but then there must be a main switch for the installation. As I interpret it.

Although probably not best practice table 53.4 (old regs, might have changed under BYB, only have old regs at work digitally - wish I could find a digital BYB pdf....) specifies that a BS 88 series fuse can be used for isolation, so wouldn't this technically be your main point of isolation for both boards?

As I said, not best practice surely, but an install as such would still comply?

EDIT 1: (Except in a TT install where isolation requires disconnection of both line and neutral?)

EDIT 2:


537.1.3 Each installation shall have provision for disconnection from the supply.
Where the distributor provides a means of disconnection complying with Chapter 53 at the origin of the installation
and agrees that it may be used as the means of isolation for the part of the installation between the origin and the
main linked switch or circuit-breaker required by Regulation 537.1.4, the requirement for isolation and switching of
that part of the installation is satisfied.
 
Last edited by a moderator:
Although probably not best practice table 53.4 (old regs, might have changed under BYB, only have old regs at work digitally - wish I could find a digital BYB pdf....) specifies that a BS 88 series fuse can be used for isolation, so wouldn't this technically be your main point of isolation for both boards?

As I said, not best practice surely, but an install as such would still comply?

(Except in a TT install where isolation requires disconnection of both line and neutral?)
Needs to isolate both live conductors IE line and neutral.
 
My interpretation of 537.1.4 is that there should be one point of isolation for the installation.

A main switch at the origin.

The double pole switches in the consumer unit are the main switch for that consumer unit but then there must be a main switch for the installation. As I interpret it.

Be that as it may IET guidance (in the Guidance Notes) specifically states that if there are multiple distribution boards it may be taken to be more than one installation, and therefore no overarching isolator is necessary.

So at best it is debateable whether a main main switch is required in front of the sub main switches.
 
Could you point me to the regulation for this as I'm struggling to see where it says that? Thanks

Haven't the good book on me at present but if you read it it is clearly stated that for a domestic premises all live conductors must be interrupted. That is why domestic distribution boards come with double pole main switches regardless of earthing arrangement.
 
haven't the good book on me at present but if you read it it is clearly stated that for a domestic premises all live conductors must be interrupted. That is why domestic distribution boards come with double pole main switches regardless of earthing arrangement.

duplicate - deleted
 
Last edited by a moderator:
Haven't the good book on me at present but if you read it it is clearly stated that for a domestic premises all live conductors must be interrupted. That is why domestic distribution boards come with double pole main switches regardless of earthing arrangement.

Just read it in the OSG - very first point in there. It seems I was getting crossed wires between single-phase and three-phase then.

EDIT: Also Reg 537.1.4:

A main switch intended for operation by ordinary persons, e.g. of a household or similar installation, shall interrupt
both live conductors of a single-phase supply.

I think I was stumbling at "well an ordinary person wouldn't pull a supply fuse so it's fine to be single pole" because the CU isolation is at each CU, and the main isolation (for a spark, not an ordinary person) would be the supply fuse.

Ignore me, getting in a tizz over nowt.
 
In many instances if there are two supplies, the second supply is intended for emergencies where the first supply has stopped.
Having an isolator which disconnected both supplies could actually be a danger.
 
So how would the single point of isolation be applied to this E7 install, note the suppliers seals on the henley blocks and the contactor. This may be partially due to the contactor coil feed being unmetered. 20160109_105710.jpg
 
So how would the single point of isolation be applied to this E7 install, note the suppliers seals on the henley blocks and the contactor. This may be partially due to the contactor coil feed being unmetered. View attachment 31148

Precisely why these interpretations that a DP switch are needed are misleading.

If some body is going to dabble with the electricity and they don't have the knowledge or competence to ensure that the correct circuit(s) are isolated then they shouldn't be doing it.

Just saying.
 

Reply to Warning label in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
496
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi everyone, a landlord is converting a house into two flats and wants a separate consumer unit for both flats upstairs and downstairs. He also...
Replies
13
Views
1K
Hi. Quick question, tightening torque for 25mm 6491x meter tails into a Henley block, anyone know or would it most likely be just FT? The Henley...
Replies
4
Views
321
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
900

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top