I know that after the Henley Block which houses the Service Mains fuse, the Voltage is 230v

If we was to remove the fuse and Measure the incoming Live wire, would the Voltage still be 230v?

ok.jpg
 
In short, yes the voltage will be the same.
However, there may be other terminals available inside the service head that provide other phases and the voltage between them will be around 400v
also a fuse that is running close to its current limit will have a small but measurable voltage drop across it.
 
For most purposes they are the same.

Typically such a fuse might dissipate around 6W at full load so if you were running at 60A (what looks like the maximum for your picture) then there would be about 0.1V drop over the fuse. You are unlikely to be able to measure that in practice as no access to the fuse terminals while live!
 
Hello guys, thanks for the answer.

james
1) is the service head the more square box with the 2 cylinders on the side under the two henley blocks?
2) if this is a common residential single phase, wouldn't the line incoming always be around 240v give/take 5%?

littlespark and timhoward
The board isnt my own, I am trying to study and take in as much as I can, and nuanced questions seem to bring some knowledge... 4am is a time I can silently focus.

tim, can you shed light on what I should be aware of?

pc1996
thanks, I was concerned with potential for much higher.


My reasoning for this question was, its commonly mentioned that the incoming phase is 60A, 80A, 100A, but apparently under the fuse the connection back to the sub can go to 400A - 800A, So I wanted to confirm if something similar occurred with the voltage... Apparently not.
 
tim, can you shed light on what I should be aware of?
Two main things came to my mind when I saw that.
That service head design is a type that could incorporate a fuse on the Neutral as well as on the incoming phase. These haven't been allowed since the mid-1950s according to my notes. The main danger being that if a N fuse pops then everything Neutral in the installation becomes live (in simple terms as there is no way 'back' for the current)

It's highly likely by now that it has a solid link inside and not a fuse, but if it was a supply that hasn't been touched for a while I'd be mentioning it to the DNO to cover myself.

The other thing is that the way the main earth is connected is not a permitted method, those clamps are designed for bonding pipework and should not be used for creating a TNS earth connection.

I'd also be checking if the tails are single insulated just in case.
 
That service head design is a type that could incorporate a fuse on the Neutral as well as on the incoming phase.
IMO that is a dedicated neutral block that cannot take a fuse. On these Series 3's they are similar in style but different shapes; the neutral block is flatter.

In any case I think this is a mock-up, not a real live intake. Neither the head nor the meter are sealed, there's no test sticker on the meter, the chipboard looks newish but the service cable couldn't have been threaded through a hole (and cable-tied from the other side) without disconnecting and then that head (and Wylex board) would likely have been replaced. And the cable itself looks like a piece of SWA wrapped in S/A tape. It's all a bit artificial.
 
It is a mock up. How old is the photo?
It seems like an example of a 50's or 60's job, except for the cable earth connection.
The earth bar is new, still find those small bars with bolts and cables shaped round for fixing.

As well as everything else, poking about with an uninsulated driver isn't a good example for students.
 
Last edited:

Reply to What is the incoming Voltage Before and After the Service Fuse? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Having a challenge understanding the concept behind why when you measure across line and neutral (live circuit) using voltage indicators we have...
Replies
25
Views
1K
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
I’m not working on this… not yet anyway, but can someone tell me why there’s a fuse or a link on the earth here? The green wire is bonded to...
Replies
3
Views
285
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Replies
12
Views
561
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock