This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main using 4mm Flat Twin and Earth. A lot of properties I've noticed have been wired with 2.5mm FTE and both connected through originally a 30amp fuse or more lately a 32amp mcb. My question is what's the maximum amperage that each size of cable can carry?
 
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main using 4mm Flat Twin and Earth. A lot of properties I've noticed have been wired with 2.5mm FTE and both connected through originally a 30amp fuse or more lately a 32amp mcb. My question is what's the maximum amperage that each size of cable can carry?
Is this cable stranded or solid ?
 
It may have been designed that way to meet volt drop, R1+R2 values etc based on using a 30A OCD?
4mm will under right circumstances allow greater ccc than 30A but that’s not a reason to exceed the current OCD.
 
The house I'm living in now was built in the 1960's and has a ring main using 4mm Flat Twin and Earth.

How old is this cable, could you post up a picture of it?
At that age it may be imperial sized cable which was physically bigger and the equivalent of modern 2.5mm is physically the same size as modern 4mm
 
How old is this cable, could you post up a picture of it?
At that age it may be imperial sized cable which was physically bigger and the equivalent of modern 2.5mm is physically the same size as modern 4mm
He says it's copper coloured, so that suggests metric, in which case it wasn't made in the sixties.
 
From that period could easily be copper clad aluminium as the used sizes were 1.5 solid and 4.0 stranded or nearest imperial equivalent.
 

Reply to What maximum amperage for cables in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I had an interesting little job this morning. Three sockets in an extension were not working and haven't worked for quite some time (years). It...
Replies
0
Views
272
Hello All Strange question for you, I know you don’t have crystal balls :) but can anyone give me any clue on the following… I have mid eighties...
Replies
8
Views
1K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
777
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
442

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock