So if they have TNS or TT then I can use the installation earth?Many people plug in their caravans without thought for this, but if you are providing a supply specifically for a caravan then yes, it shouldn't be connected to a PME earthing setup.
Regarding why:
On a TNCS earthed supply there can be a difference in potential between the combined installation Neutral and Earth and real earth due the return neutral current.
Inside a house this is relatively safe.
Outside there are two particular scenarios to consider:
1 - standing on real earth and touching anything earthed can give a tingle. Not dangerous, but un-nerving!
2 - very rare scenario, but if the supply Neutral breaks, then worst case the turn Neutral current goes to the cutout, is linked to earth, and is then looking for a return path through everything that is earthed. The degree to which it will find one depends on each unique situation, e.g. whether there's a metal bonded water pipe. But standing outside on real earth and touching anything earthed is worst-case putting 230v between your hand and your feet with you in the middle as you could be the return path.
So on caravan sites, and supplies to caravans, the installation earth is not connected to the caravan earth, to avoid these scenario's happening.
I'm not sure I would agree with this interpretation, at it says "caravan parks, camping parks, and similar locations", all of which are open to the public.I don’t have regs here but I thought section 708 scope was worded vaguely and one interpretation was it could apply to any situation where supply has provided for a caravan even if it wasn’t on a caravan park. Very happy to be proved wrong though!
I (obviously) defer to anyone that has the regs open especially as I’m in a pub!I'm not sure I would agree with this interpretation, at it says "caravan parks, camping parks, and similar locations", all of which are open to the public.
However there would be no harm in applying the requirements of this section to a caravan supply on private ground.
The main part that would apply is the prohibition on the use of a PME supply.
What, you don't take your regs into the pub! Shame on you.I (obviously) defer to anyone that has the regs open especially as I’m in a pub!
Maybe the OP can clarify the exact circumstances.
Not tonight! I’m in proud dad mode as my teenage daughter has a gig and is doing great!What, you don't take your regs into the pub! Shame on you.
Technically yes, but many "TN-S" supplies are actually off segments with a PME conductor, just they look separate at the DNO cut-out.So if they have TNS or TT then I can use the installation earth?
The two issues with using the SWA armour are:Also for the cable I'm probably gonna use 3 core 10mm SWA. But what if I used 2 core and used the armouring as the main earth? Crazy talk?
Does anyone have a reply to this?So if they have TNS or TT then I can use the installation earth?
Also for the cable I'm probably gonna use 3 core 10mm SWA. But what if I used 2 core and used the armouring as the main earth? Crazy talk?
Yet again you have came to answer stuff. Thanks pcTechnically yes, but many "TN-S" supplies are actually off segments with a PME conductor, just they look separate at the DNO cut-out.
Personally I would TT it unless the main supply was already TT.
The two issues with using the SWA armour are:
See also this article:
- If using a 16A or 32A "commando" socket you will struggle to have any reliable connection to the armour. For hard-wiring to a fixed unit with glands no problem
- The end of cable Zs for disconnection has to be met. For TT supply (RCD before the SWA run) then no problem as RCD will disconnect on any sort of armour impedance, but if TN to the caravan point you ought to check it is met.
Electrical installations in caravan/camping parks, caravans and motor caravans
As the warmer weather approaches and with summer around the corner, thoughts turn to holidays. Chief Engineer Geoff Cronshaw reminds us of the requirements of BS 7671:2008+A3:2015.bit.ly
Sorry it's a static. And about 30m run I'm cableStill like to know if this is for a tourer or a static…. But the 10.0mm mentioned on #3 suggests something big.
How’s the wording of the regs on this?
I’m sure it says a rod for a caravan park, not for just a caravan plugged into a house…
So if they have TNS or TT then I can use the installation earth?
Also for the cable I'm probably gonna use 3 core 10mm SWA. But what if I used 2 core and used the armouring as the main earth? Crazy talk?