Discuss Zs from board supplying another board in the UK Electrical Forum area at ElectriciansForums.net
Ze is only at the origin, the rest are Zs.
Measure/calculate the R1+R2 for each distribution circuit and add the Ze. (Zs=Ze+(R1+R2))
I have a ccu with a Ze of 0.09 and it's supplying another ccu which that board supplies multiple other CCUs I was wondering how I would work out my zs and ze on the other boards?
Ze only exists at the origin, e stands for external.
In an existing installation you measure Zs at each board.
If this is at the design stage then you need to use the calculated impedance of the circuit and add it to the Ze quoted for the supply.
Does it not become Zs at DB? from board to board, I hear what you're saying, but does my statement not hold water in this case?
Yes it does become the Zs at the DB, but obviously that is also the Zs of the distribution circuit because they are one and the same thing.
Strictly speaking 'Zs at DB' or 'Zdb' are not correct terminology, much like 'ring main' instead of 'ring final circuit', everyone knows what is meant by it, it's commonly used, but it's not correct terminology.
Each board would have its own Zs, sometimes referred to a Zdb. I think we're saying the same thing.
But, 'Zs at DB1, 2, 3', whatever, is a statement...nothing wrong with the terminology, whatsoever.
I agree with ipf, but there will always be a Jobsworth that disagrees with this though.
Bit of Confusion there, Someone did tell me I have to do the Ze test with all Parallel paths even at origin seems a bit pointless.
You do your PEFC with all parallel paths connected at the origin not a ZE test .The Ze test determines the resistance of the earthing conductor external to the installation and confirms an earth connection to the installation hence it’s done with no parallel paths connected.
If it's the origin CUU does anything need to go into
"Zs at DB" on the "Schedule of test results" form ?
I'm talking about Schedule of test result - Zs at DB
ill just take it you don't have to do Zs at DB at origin DB, unless anyone says differently.
The test carried out at the origin DB is the Ze not Zs. This is done with parallel paths removed to confirm the continuity and loop impedance of the DNO supply.
Zs is done with parallel paths in place on distribution and final circuits to ensure the installation disconnection times can be met.
Reply to Zs from board supplying another board in the UK Electrical Forum area at ElectriciansForums.net
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...