anyone come across this before zs at board 0.28. then when measure zs on rcd side on live and neutral, reading of 0.77. from the same earth position.?, ie got a socket a meter away from board earth loop 0.81. measure earth from socket to board its 0.02.
 
RCD affecting reading.
 
that's nothing. i once has a RCD adding 149 ohms to the Zs. took me almost an hour to suss it out,
 
Isn't this called RCD uplift? Where the RCD is affecting the reading
 
Isn't this called RCD uplift? Where the RCD is affecting the reading
and so the thread degenerates into ladies' underwear.;);)
 
I think that the "no trip" feature of the test meter sways the Zs readings.. my Metrel is about half an ohm different.
 
  • Agree
Reactions: Jim_e_Jib
I'll think you'll find that this will be case with MK RCD's... got caught out this myself. EFLI testing on the supply side would give similar value to that of Ze but Zs was nearly 1 ohm.. turns out that the RCD was adding excess of 0.70-0.80 ohms.

It's a combination of RCD and testers no trip circuitry on my mft1552.

True Zs results can be calculated by subtracting the reading of the RCD input from the outputs and then subtracting that result from your sub circuit Zs.
 
  • Agree
Reactions: Michael J
Isnt there a resistance from the coil in an rcd that ups the reading?
 
  • Informative
Reactions: Chris1477
I'll think you'll find that this will be case with MK RCD's... got caught out this myself. EFLI testing on the supply side would give similar value to that of Ze but Zs was nearly 1 ohm.. turns out that the RCD was adding excess of 0.70-0.80 ohms.

It's a combination of RCD and testers no trip circuitry on my mft1552.

True Zs results can be calculated by subtracting the reading of the RCD input from the outputs and then subtracting that result from your sub circuit Zs.
yes mine is the mft 1730 and mine is adding about .5/.6 ohms, just tried it at my house with a wylex rcd and getting about 0nly .1 ohm.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
zs readings before and after rcd.
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
14

Advert

Thread statistics

Created
gjcone44,
Last reply from
gjcone44,
Replies
14
Views
3,479

Advert