Discuss zs readings before and after rcd. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
anyone come across this before zs at board 0.28. then when measure zs on rcd side on live and neutral, reading of 0.77. from the same earth position.?, ie got a socket a meter away from board earth loop 0.81. measure earth from socket to board its 0.02.
that's nothing. i once has a RCD adding 149 ohms to the Zs. took me almost an hour to suss it out,
I'll think you'll find that this will be case with MK RCD's... got caught out this myself. EFLI testing on the supply side would give similar value to that of Ze but Zs was nearly 1 ohm.. turns out that the RCD was adding excess of 0.70-0.80 ohms.
It's a combination of RCD and testers no trip circuitry on my mft1552.
True Zs results can be calculated by subtracting the reading of the RCD input from the outputs and then subtracting that result from your sub circuit Zs.
yes mine is the mft 1730 and mine is adding about .5/.6 ohms, just tried it at my house with a wylex rcd and getting about 0nly .1 ohm.
Reply to zs readings before and after rcd. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Anyone come across this before? I was asked to do a Zs on a 3ph surge device; L1 was around 6 ohm, L2 & L3 around 0.11. Wired in singles from a...
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...