HI
Ive just installed a new board in a garage on 12mtr 6mm 3c swa and when testing im scratching my head
ive got
Ze of .34 at the main db -tested
Zs of .74 at the garage db - tested "sometimes its up and down"
and a R1 + R2 at of the swa as .10
to me this is way out ,does anyone know what the problem could be ?
Could be an accuracy problem due to the low current test, I know I get that a lot.
Could also be a high internal resistance of the RCD so you could try and rule that out first.