Discuss terminating tt tails in the UK Electrical Forum area at ElectriciansForums.net
N
nicademus
Hello what is the (proper) way to terminate SWA tails into amendment 3 metal consumer unit, & its s type time delay protection at meter cabinet on a TT system. Fair size new build so C.U is about 12 mtrs from cabinet. (Excuse if I've left any details out.).
Hi thanks for the quick reply Dave sparks, should have said the SWA tails will be going into the back of CU. And of course
The termination query refers to mainly the earthing of the wired armour earth, is it Right to earth enclosure on a TT? Many thanks and sorry for ineptness of original post.
Not sure how you are going to avoid that using an AMD3 compliant enclosure!
SWA must be glanded into the top or bottom of the metal CU.
can do, but an extra box stuck on the wall may be unacceptable to fussy knickers customer.
Accessible for gland connections I assume you mean ? Usually use 3 core - lne and a flying lead for armourings no connections in box just inner sheath into db with fly lead
rather have gland where it's accessible for routine maintenance ( check tightness etc.) . you beginning to sound like a customer ( want it to work, but don't want to see it ). :tounge_smile:
had one like that the other week. when they said as cheap as possible, i offered to get them some scrap cable and some second hand sockets with a bit of paint on. that shut them up.
The answer is still SWA gland whatever direction it comes from.
As for the question about earthing the enclosure, that is quite frankly a very scary question indeed as the earthing of metal enclosures is one of the most basic safety provisions
Hi davesparks, understand that earthing a metal enclosure is basic provision but with regards to CU and TT set up and the new 3rd amd not quite so convinced, other contributors suggestion more helpful.
Reply to terminating tt tails in the UK Electrical Forum area at ElectriciansForums.net
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
5K
I have added a consumer unit and an earth stake to this so called temporary supply. This is a full rcbo board apart from the mcb to the spd...
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...