Is it acceptable to use a redundant 30A cooker circuit wired in 6mm, and downsize to 4mm via JB for a kitchen radial?
For example, if there is one ring supplying a house and you would like to reduce the risk of overloading with all the kicthen appliances.
Obviously new circuit is the best option but would this be acceptable?
Cheers
Hi there.
Cheers
What sort of JB do you intend to use, and will it be accessible?
but if a trapdoor is fitted, with the carpet cut and gripper strip applied around the access point? when will the iet define what is accessible? will this be a new edition, another £75.?
The 6mm cable tests out fine. Will be used to supply 4 double sockets and a fcu on a kitchen so not a big load.
It's just an alternative to pulling in a new circuit and also prevents the risk of overloading with the house on one ring.
Needs RCD protection.
Can you get a maintenence free JB for 6mm ?
wago do a 6mm 40A connector. it's how you interpret M/F includeing the enclosure.
Ideal, just found the wagos.
Wago do the maintenance free JB's but I'm guessing a 6mm and 4mm won't fit easily.
Would you say that this wiring method (with MF JB) is an acceptable alteration?
The only other way other than new circuit or massive alteration is to keep the kitchen on the ring. I'm just concerned about overloading.
By my reckoning, with a rewirable fuse the 6mm isn't gonna cut it on a 30A OCPD, let alone a 4mm. You might get away with it on a 20A OCPD depending on your calcs.
I would be concerned about the apparent going ahead with this without cable calcs for this alteration. My initial suspicion is that the alteration as you have described will not be suitable or compliant.
Crikey how did we get to this stage it only started off as a discussion topic, now it looks like the OP is actually doing the job.
So the new regs state that a 4mm radial can be used with bs 3036 OCPD?
So what I proposed to do is perfectly acceptable?
The regs say that cable size is to be determined by calculation. If you do one you will find out whether it complies or not.
Hint: You will find that it won't.
Unless the yellow book is amended, but if it's same as green osg, then yes IMO.
I have the green book and it states you can on bs 3036, so I stand corrected.
Not in table 7.1 which is referenced under table H2.1. Contradictory information as always. Table 7.1 states that the minimum size is 6mm for BS3036 at 30A and only if installed in method C.
Cf will always change cable calcs dramatically so quite how the onsite guide thinks an all encompassing table for all OCPDs and all installation methods will work is beyond me
Yellow osg, not permitted
it's the dumbing down syndrome. just bung in a cable big enough for the worst case scenario, no need to do calcs. a bit like fitting 25mm tails after a 60A DNO fuse,
Ok so by replacing the BS3036 with a Wylex plug in 60891, it would then comply?
There are many possible variables that would allow the arrangement to comply. It's up to the designer to choose the most appropriate method of doing so for the use, situation, installation method, and practical application of installation for the circuit.
I notice you are an apprentice. You should get your head into some calculations to find out what will and won't comply for your own education.
I've read the tables in the yellow OSG and 6mm complies with bs3036 but 4mm doesn't.
60898 does comply.
The current carrying capacity is acceptable for 4mm.
The length of circuit is approx 30 metres and will be supplying 5 double sockets. It's clipped direct.
The only issue I can see is the protective device.
60898 does comply.
Method c only.
Method C is also applicable to multicore cables buried direct in non thermally insulated walls and also under capping buried in non thermally insulated walls. You could technically class oval conduit as method B I suppose though.
Don't know about method b conduit or trunking on wall not in wall. lol
Reply to Redundant 6mm Cooker circuit to 4mm radial? in the UK Electrical Forum area at ElectriciansForums.net
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
I've been asked to change few double sockets, but not keen on touching after seeing 6mm cable, so did a bit of checking as can see the kitchen...
4K
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...