Discuss Redundant 6mm Cooker circuit to 4mm radial? in the UK Electrical Forum area at ElectriciansForums.net
N
Noob2013
Hi there.
Just a discussion with a colleague.
Is it acceptable to use a redundant 30A cooker circuit wired in 6mm, and downsize to 4mm via JB for a kitchen radial?
For example, if there is one ring supplying a house and you would like to reduce the risk of overloading with all the kicthen appliances.
Obviously new circuit is the best option but would this be acceptable?
Cheers
Hi there.
Cheers
What sort of JB do you intend to use, and will it be accessible?
but if a trapdoor is fitted, with the carpet cut and gripper strip applied around the access point? when will the iet define what is accessible? will this be a new edition, another £75.?
The 6mm cable tests out fine. Will be used to supply 4 double sockets and a fcu on a kitchen so not a big load.
It's just an alternative to pulling in a new circuit and also prevents the risk of overloading with the house on one ring.
Needs RCD protection.
Can you get a maintenence free JB for 6mm ?
wago do a 6mm 40A connector. it's how you interpret M/F includeing the enclosure.
Ideal, just found the wagos.
Wago do the maintenance free JB's but I'm guessing a 6mm and 4mm won't fit easily.
Would you say that this wiring method (with MF JB) is an acceptable alteration?
The only other way other than new circuit or massive alteration is to keep the kitchen on the ring. I'm just concerned about overloading.
By my reckoning, with a rewirable fuse the 6mm isn't gonna cut it on a 30A OCPD, let alone a 4mm. You might get away with it on a 20A OCPD depending on your calcs.
I would be concerned about the apparent going ahead with this without cable calcs for this alteration. My initial suspicion is that the alteration as you have described will not be suitable or compliant.
Reply to Redundant 6mm Cooker circuit to 4mm radial? in the UK Electrical Forum area at ElectriciansForums.net
I've been asked to change few double sockets, but not keen on touching after seeing 6mm cable, so did a bit of checking as can see the kitchen...
4K
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...