Crikey how did we get to this stage it only started off as a discussion topic, now it looks like the OP is actually doing the job.
 
So the new regs state that a 4mm radial can be used with bs 3036 OCPD?

So what I proposed to do is perfectly acceptable?

The regs say that cable size is to be determined by calculation. If you do one you will find out whether it complies or not.
Hint: You will find that it won't.
 
Unless the yellow book is amended, but if it's same as green osg, then yes IMO.

I have the green book and it states you can on bs 3036, so I stand corrected.

Not in table 7.1 which is referenced under table H2.1. Contradictory information as always. Table 7.1 states that the minimum size is 6mm for BS3036 at 30A and only if installed in method C.

Cf will always change cable calcs dramatically so quite how the onsite guide thinks an all encompassing table for all OCPDs and all installation methods will work is beyond me
 
3b2805ed63b676b506e4775bc1f05d86.jpg


Yellow osg, not permitted
 
it's the dumbing down syndrome. just bung in a cable big enough for the worst case scenario, no need to do calcs. a bit like fitting 25mm tails after a 60A DNO fuse,
 
Ok so by replacing the BS3036 with a Wylex plug in 60891, it would then comply?

There are many possible variables that would allow the arrangement to comply. It's up to the designer to choose the most appropriate method of doing so for the use, situation, installation method, and practical application of installation for the circuit.

I notice you are an apprentice. You should get your head into some calculations to find out what will and won't comply for your own education.
 
I've read the tables in the yellow OSG and 6mm complies with bs3036 but 4mm doesn't.

60898 does comply.

The current carrying capacity is acceptable for 4mm.

The length of circuit is approx 30 metres and will be supplying 5 double sockets. It's clipped direct.

The only issue I can see is the protective device.
 
I've read the tables in the yellow OSG and 6mm complies with bs3036 but 4mm doesn't.

60898 does comply.

The current carrying capacity is acceptable for 4mm.

The length of circuit is approx 30 metres and will be supplying 5 double sockets. It's clipped direct.

The only issue I can see is the protective device.
Method c only.
 

Reply to Redundant 6mm Cooker circuit to 4mm radial? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
808
I've been asked to change few double sockets, but not keen on touching after seeing 6mm cable, so did a bit of checking as can see the kitchen...
Replies
19
Views
4K
Hi all Some advice on this would be great. Due to wire a kitchen from scratch and in a pickle over the designing of the oven and hob circuits due...
Replies
6
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock