I have the green book and it states you can on bs 3036, so I stand corrected.
Crikey how did we get to this stage it only started off as a discussion topic, now it looks like the OP is actually doing the job.
It was a discussion about a job I will be doing. Colleague wasn't too sure so we were debating
Unless the yellow book is amended, but if it's same as green osg, then yes IMO.So the new regs state that a 4mm radial can be used with bs 3036 OCPD?
So what I proposed to do is perfectly acceptable?
So the new regs state that a 4mm radial can be used with bs 3036 OCPD?
So what I proposed to do is perfectly acceptable?
Unless the yellow book is amended, but if it's same as green osg, then yes IMO.
I have the green book and it states you can on bs 3036, so I stand corrected.
10mm jokes, would love to see somebody wrestling them into a socket.
Yellow osg, not permitted
Ok so by replacing the BS3036 with a Wylex plug in 60891, it would then comply?
Method c only.I've read the tables in the yellow OSG and 6mm complies with bs3036 but 4mm doesn't.
60898 does comply.
The current carrying capacity is acceptable for 4mm.
The length of circuit is approx 30 metres and will be supplying 5 double sockets. It's clipped direct.
The only issue I can see is the protective device.
Method c only.
Yes I would agree with thatThe cable run is through partition from c.u, under the floorboards with no insulation and then in oval conduit buried in plaster.
So reference method c?