A client contact me as they are getting the supply upgraded to a block of flats and UKPN need a figure adjusted for diversity for each flat.
The original contact didn’t give a crap about the supply capacity.

x6 flats have been refurbished and during this process x6 15kw electric boilers for each flat has been added. (No gas in flats).

The issue I am having is after diversity from the OSG I am getting a crazy number per flat (150a roughly) or maybe I am missing something.

With my calculations I feel I am overkill and a substation will need to be installed, how common are the electric combi boilers as they are a big problem and not accounted for by the original fit out contractors, I am close to telling client they can’t have them and need an alternative as a substation is 100k

UKPN have said you need a sub station installing if each flat consumes 150a... these bloody boilers, I suppose it’s not my problem but I want to feel I am being realistic with my advice atleast.

Each flat DB is the following:
CCT1 Boiler supply 63a
CCT2 Ring 1 32a
CCT3Ring 2 32a
CCT4 lights 1 6a
CCT5 lights 2 6a
CCT6 Oven 40a
CCT 7 Hob 16a
 
Are you applying diversity to the MCB rating or to what is actually going to be installed?
 
I am going by MCB with the exception of the boiler circuit as it’s 15kw on a 63a breaker.

Well at least do it properly. If there is say 5 LED pendants on that lighting circuit that could be 15w (0.07A) and you are putting that as 4A (66%).

Same for sockets. Why put through 20A for a ring final when in all honesty the installation is probably going to be half that for both rings.
 
Ifeel your pain with this, load calculations are the thing i feel least confident with. When ever i follow OSG diversity theyre always "overloaded" its then a case of rationalising to get the number down which feels like a fiddle.

Is this MCB undersized for 15kW? I get that to 65A.
 
  • Agree
Reactions: suffolkspark
Hi - the 15kW water boiler is a big boy and if I recall correctly we're not given any diversity allowance for heaters. Modern electric boilers can be limited to a max kW by config and manufacturers quote times for hw heating (like 6 min for 50l at 15kW and 30min at 3kW).

Can I ask what make and model is used?
 
40A looks a lot for the oven, most new ovens are pretty efficient, spec a 13A connection and and must be A or B energy rated. It would be reasonable to use that for the calcs.

The boilers are the problem, bit late now but heat pumps might have been a solution. There's a thread on the same subject here..
 
I have same problem
1st fixed 14x 1bed flats with 12kw boiler in each

I calced max demand around 72a per flat so would of thought looking at a 245kva new supply

however SSEN are saying they want to install a 130KVA supply and it will be enough

I have installed the 14x switch fuse isolators (luckily the Lewden ones come with 60 80 and 100a fuses and all sub mains are 25mm 3core

and SSEN are supplying/fitting the Ryefield

So up to them if they want a callout for a popped main head!

I have it all in writting via email so its their call now
 
I always do 100% demand of the largest load in this case the boiler then add 40% of the remainder, having applied diversity to the remaining circuits first.
 
however SSEN are saying they want to install a 130KVA supply and it will be enough

SSEN will be applying diversity to the whole block of flats, something they are probably quite experienced at.
 
  • Agree
Reactions: Ian1981
Of corse wilko thank you.

Gabarron MAC15

I am thinking about asking a heating engineer to dial them all down to 3kw and see if they even work, that’s the only way I would feel comfortable
 
diversity, sod it ..bang it in .:D
 
  • Agree
Reactions: snowhead
Maybe a stupid question but...

On new installs...

With the advent of low power appliances is there more sense in putting rings on 20A MCB ( mad but just for discussion, using 1.5 T&E)

On a typical install with up/down and kitchen sockets, instead of diversified 32+(32*0.4)+(32*0.4)=57.6A you have 20+(20*0.4)+(20*0.4)=36A.

Please destroy by all means but interested in the reasons why not.
 
With the advent of low power appliances is there more sense in putting rings on 20A MCB ( mad but just for discussion, using 1.5 T&E)
I get the point why don't they use 1.0mm instead .;)its is called resistance .don't fight it .the bigger the cable the more flow of current .
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
london
Business Name
Platinum electrical

Thread Information

Title
Maximum demand question
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
chris day,
Last reply from
buzzlightyear,
Replies
15
Views
2,720

Advert