Thoughts required on todays scenario .
Commercial premises fed from 100 amp 3 phase TNS supply ZE 0.40
feeds 80 amp 3 phase switch fuse (max zs 0.57)
feeds 400 amp mainswitch protek panel in 35mm swa 16mm earth
125 amp mccb (0.24 max zs) submain exceeds max zs at 0.57
Had this down as a code 2 but max zs of 80 amp switch fuse will disconnect in under 5 seconds ....
Dogs dinner of a set up , any one in agreement of my code 3 ????