currently working through a EICR on a empty care home soon to be refurbished and new clients to move in.
Distribution circuit from DB 1 feeding DB3( supplying sockets/ lighting etc) fed from a C type bs en 60898 mcb 63 amp.
Max zs 0.34(100% value)
Measured zs 0.34 ( over the 80% correction factor at site measured temperature)
DB 6 fed ( supplying sockets and lighting)from DB 3 on a 40 amp type C bs en 60898.
So a sub main feeding a DB feeding another submain for another DB all 3 phase.
A discrimination/ design nightmare all carried out in 2006, no EIC , electrical/mechanical or design drawings.
And they say domestic is bad!!
No questions to ask the forum, just a rant really.
 
Just been working somewhere with a similar awful design, 6 of the DBs are fed from a single RCD.
 
It’s awful.
I’ve got ring final circuits with readings of 1.86 ohms for the line and neutral conductors because they are such large cable runs and the number of points on some of the rings reach upto 56 points!
Same with the lights, some have around 40 points where around 7 bedrooms are fed from a single circuit.
 
  • Like
Reactions: suffolkspark
Get into some old industrial plants and have a look in some old control panels. No drawings, all singles, all same colour. Just a manager barking to get the thing working :)

:grinning:
Its what makes it interesting, be rubbish if everything was labelled and easy ..
 
  • Like
Reactions: Rpa07 and FatAlan
I love doing that! Perhaps without the manager bit. Last one was good fun, all red wires no wire markers, no labels on any component or the I/O terminals.
 
  • Like
Reactions: BruvDunk
Yes I see so many bad designed installations as you describe I feel your pain. I think people just think if sockets you use 2.5mm with and a 32 amp mcb or rdbo with no thought for volt drop max zs ect, and I lost count of the amount of circuits I find that have excessive earth loop impedance.:mad:
 
  • Agree
Reactions: Ian1981
currently working through a EICR on a empty care home soon to be refurbished and new clients to move in.
Distribution circuit from DB 1 feeding DB3( supplying sockets/ lighting etc) fed from a C type bs en 60898 mcb 63 amp.
Max zs 0.34(100% value)
Measured zs 0.34 ( over the 80% correction factor at site measured temperature)
DB 6 fed ( supplying sockets and lighting)from DB 3 on a 40 amp type C bs en 60898.
So a sub main feeding a DB feeding another submain for another DB all 3 phase.
A discrimination/ design nightmare all carried out in 2006, no EIC , electrical/mechanical or design drawings.
And they say domestic is bad!!
No questions to ask the forum, just a rant really.
Understand your frustration fella, I have seen similar, it happens everywhere, DBs being fed off others is a very regular thing to see, it is almost the norm,
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Poor installation practice/design
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
Ian1981,
Last reply from
MDJ,
Replies
6
Views
1,556

Advert