Hi guys been asked to put a radial in for spurs for a fire alarm panel supply is it okay to use red FP200 to carry 230v? If so or not could you tell me where I find this information in the regs ? Thanks
 
See Appendix 1 of BS7671.
Look for BS7629-1:2015 in the Table.
 
Hi guys been asked to put a radial in for spurs for a fire alarm panel supply is it okay to use red FP200 to carry 230v? If so or not could you tell me where I find this information in the regs ? Thanks
yeah as long as it is 1.5mm enhanced
 
Hi guys been asked to put a radial in for spurs for a fire alarm panel supply is it okay to use red FP200 to carry 230v? If so or not could you tell me where I find this information in the regs ? Thanks
Fire Alarm isolator switch has to be cabled in FP200 and connected directly into own RCD at distribution/consumer unit
 
Fire Alarm isolator switch has to be cabled in FP200 and connected directly into own RCD at distribution/consumer unit
It doesn't have to be FP200 I could use MICC if need be and rcd protection I would be avoiding for such a circuit conditions permitting.
 
I have taken this up with the people who make FP200 and it is rated for 230v AC apparently. I have seen a C2 for non fire rated cable supplying fire alarm panels. A new one for Codebreakers I'd imagine.
 
I don’t know where the idea it isn’t 230v rated comes from. I’ve connected so many like this, usually in trunking or clipped direct to avoid need for RCD.
(A shared RCD is the thing to avoid at all costs)
I’ve got a MICC job next week and it’s sad that I’m really looking forward to it!
 
I don’t know where the idea it isn’t 230v rated comes from. I’ve connected so many like this, usually in trunking or clipped direct to avoid need for RCD.
(A shared RCD is the thing to avoid at all costs)
I’ve got a MICC job next week and it’s sad that I’m really looking forward to it!
What is it you are doing.
 
That brings back some memories, this was one of the practical assessments we had to do at college, using the MICC through jointing kit.
micc jointing kit.jpg
 

Attachments

Last edited by a moderator:
That brings back some memories, this was one of the practical assessments we had to do at college, using the MICC through jointing kit.
Never seen one of those.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Fire alarm panel Red Fp200 230V
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
Handyapprentice4,
Last reply from
7029 dave,
Replies
11
Views
3,520

Advert