During the construction of an installation, insulation resistance tests have been carried out between live conductors and earth on the individual circuits and the L to E results are shown below. What is the expected value of insulation resistance L to E when the whole installation is tested?
can someone explain how to break down this question?
thanks
there is another with the answer
The insulation resistance of two circuits is of 40MΩ an 36MΩ respectively. When tested together what is the total insulation resistance:?
answer is 22mohms
Upvote 0
Bear in mind that when all the circuits are connected to the consumer unit, they are effectively in parallel. This should give you a clue as to how to answer the question.
Even without a calculator, there is one value that it will certainly be less than.
Upvote 0
thanks
1/Rt = 1/R1 + 1/R2 + 1/R3 + 1/R4...
Upvote 0
Thanks alos there is a similar question here
Risteard gave the formula, which becomes:
1/40 + 1/36 = 1/R which to 2 decimal places is:
0.025 + 0.028 = 1/R
Work out R from that 🤔
Consider - if the two IR figures were both 40Meg, then in parallel that would make 20Meg.
But one is a lower resistance than 40, so your answer is going to be a lower number than 20.
Upvote 0
0.025 + 0.028 = 1/R
yes thanks makes sense now
Upvote 0
0.025 + 0.028 = 1/R
so with the 0.053 you then move that 2 decimal places?
Upvote 0
bristol
2391 question multiple choice IR help to break down
sid521,
sid521,
Electrical Courses