Guest viewing limit reached
During the construction of an installation, insulation resistance tests have been carried out between live conductors and earth on the individual circuits and the L to E results are shown below. What is the expected value of insulation resistance L to E when the whole installation is tested?
can someone explain how to break down this question?
thanks
there is another with the answer
The insulation resistance of two circuits is of 40MΩ an 36MΩ respectively. When tested together what is the total insulation resistance:?
answer is 22mohms
Upvote 0
Bear in mind that when all the circuits are connected to the consumer unit, they are effectively in parallel. This should give you a clue as to how to answer the question.
Even without a calculator, there is one value that it will certainly be less than.
Upvote 0
thanks
1/Rt = 1/R1 + 1/R2 + 1/R3 + 1/R4...
Upvote 0
Thanks alos there is a similar question here
Risteard gave the formula, which becomes:
1/40 + 1/36 = 1/R which to 2 decimal places is:
0.025 + 0.028 = 1/R
Work out R from that 🤔
Consider - if the two IR figures were both 40Meg, then in parallel that would make 20Meg.
But one is a lower resistance than 40, so your answer is going to be a lower number than 20.
Upvote 0
0.025 + 0.028 = 1/R
yes thanks makes sense now
Upvote 0
0.025 + 0.028 = 1/R
so with the 0.053 you then move that 2 decimal places?
Upvote 0
No. Sorry - missed the post above!🫣
0.025 + 0.028 = 1/R
Or 0.053 = 1/R
Some basic maths here!
If 1/R = 0.053, how do you work out R? Use a calculator?
One way of explaining it - Multiply both sides of the equation by R gives 1 = 0.053R
So R = 1/0.053. That you can do on your calculator.
Or by long division, as if if anyone can remember how to do that!
Upvote 0
0.025 + 0.028 = 1/R
Or 0.053 = 1/R
thanks
also do you know where i would find the maximum permissible residual operating current for rcd on a TT system . in the bs7671 or gn3 and where about ? thanks
Upvote 0
bristol
2391 question multiple choice IR help to break down
Electrician Courses : Electrical Quals
sid521,
sid521,
Electrical Courses