During the construction of an installation, insulation resistance tests have been carried out between live conductors and earth on the individual circuits and the L to E results are shown below. What is the expected value of insulation resistance L to E when the whole installation is tested?
can someone explain how to break down this question?
thanks
What are the four multiple choice answers?
Upvote 0
didnt show answer :(
Upvote 0
there is another with the answer
The insulation resistance of two circuits is of 40MΩ an 36MΩ respectively. When tested together what is the total insulation resistance:?
answer is 22mohms
Upvote 0
Bear in mind that when all the circuits are connected to the consumer unit, they are effectively in parallel. This should give you a clue as to how to answer the question.
Even without a calculator, there is one value that it will certainly be less than.
Reactions: sid521
Upvote 0
For multiple choice there should be four answers. As above, with the answers you will require no calculation although it can be done by calculation.
Reactions: sid521
Upvote 0
ah yes is it the median 130 value divided by the number of circuits 4 so 130 divided by 4 equals 32.5 (correct on multiple choice) thanks
Upvote 0
thanks
1/Rt = 1/R1 + 1/R2 + 1/R3 + 1/R4...
Upvote 0
33.6mohms is correct answer
32.23 Megohms unless I punched something in incorrectly. Probably just a rounding error actually. (Maybe they were only going to 2 decimal places or something at each step.)
Upvote 0
Thanks alos there is a similar question here
Upvote 0
Risteard gave the formula, which becomes:
1/40 + 1/36 = 1/R which to 2 decimal places is:
0.025 + 0.028 = 1/R
Work out R from that 🤔
Consider - if the two IR figures were both 40Meg, then in parallel that would make 20Meg.
But one is a lower resistance than 40, so your answer is going to be a lower number than 20.
Reactions: westward10
Upvote 0
0.025 + 0.028 = 1/R
yes thanks makes sense now
Upvote 0
0.025 + 0.028 = 1/R
so with the 0.053 you then move that 2 decimal places?
Upvote 0
No. Your answer is 1 over 0.053, so you need to calculate that.
Upvote 0
No. Sorry - missed the post above!🫣
0.025 + 0.028 = 1/R
Or 0.053 = 1/R
Some basic maths here!
If 1/R = 0.053, how do you work out R? Use a calculator?
One way of explaining it - Multiply both sides of the equation by R gives 1 = 0.053R
So R = 1/0.053. That you can do on your calculator.
Or by long division, as if if anyone can remember how to do that!
Upvote 0
0.025 + 0.028 = 1/R
Or 0.053 = 1/R
thanks
also do you know where i would find the maximum permissible residual operating current for rcd on a TT system . in the bs7671 or gn3 and where about ? thanks