Hi guys,
EICR
Have a 125a cammando socket protected by a 100amp 100ma RCCB at the unit and it’s OCPD is the fuses in the cut out rated at 100a.
Everything is within 3 meters.
System is TT.
Firstly is this rating of RCCB and supply suitable for socket? If not how would it be coded?
Secondly does this socket needs its own OCPD and isolator? If not how would it be coded?
Any help on this matter would be much appreciated.
The rating of the RCD should be dictated by the protective device unless the RCD is actually an RCBO. As it exists the protective devices are the 100A fuses at the service head so the RCD is fine but yes it should not be relying on these fuses so I would Code 2 it.
Is it potentially dangerous if the Service Fuse blows ? Poor set up but I think C3
Only if the DNO agree to it (part 4)
434.3 Omission of devices for protection against fault current
A device for protection against fault current need not be provided for: (i) a conductor connecting a generator, transformer, rectifier or an accumulator battery to the associated control panel where the protective device is placed in the panel
(ii) a circuit where disconnection could cause danger for the operation of the installation concerned, such as those quoted in Regulation 433.3.3
(iii) certain measuring circuits
(iv) the origin of an installation where the distributor installs one or more devices providing protection against fault current and agrees that such a device affords protection to the part of the installation between the origin and the main distribution point of the installation where further protection against fault current is provided,