Discuss OSG. Page 33. Is this right? in the Australia area at ElectriciansForums.net

S

simonspark

Hello all.
The other day I was leafing through the red OSG and for no reason started to read chapter 5, isolation and switching. At point ii for every other circuit it says blah blah blah......... The device must switch all live conductors in a TT system and all line conductors in a TN system.
The latter point I have no problem with. It's the former. Does this mean ( you should read the full paragraph to be honest. I couldn't be bothered to type it!) that in a TT system all circuit breakers should be double pole? It certainly reads that way in my eyes.
I rarely have any dealings with TT systems, so I don't get involved. But one day I may need to know the answer to this. Anyone?
Simon
 
No. It doesnt say that. Thats what I always thought. Ok, I'm gonna type out the whole bloody thing.
ii Other than at the origin of the installation, every circuit or groups of circuits that may have to be isolated without interrupting the supply to other circuits should be provided with it's own isolating device. This device must switch all live conductors in a TT system and all line conductors in a TN system.

See what I mean?
 
every circuit or groups of circuits that may have to be isolated without interrupting the supply to other circuits should be provided with it's own isolating device.

Do any circuits need to have the facility to isolate without isolating other circuits though?
 
Risteard. Sorry mate but Ive already typed this once before and I don't know where it went! But as I tried to say (puff!) Yes. According to the wording of the paragraph. It also cross references Regulation 537.2.1.1. Whatever that may be
 
New posts

Reply to OSG. Page 33. Is this right? in the Australia area at ElectriciansForums.net

Similar Threads

I haven't seen a lot of discussion on this subject and have questions pertaining to isolation where TN earthing is present and any peculiarites...
Replies
21
Views
830
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
375
I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
859

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top