The other day I was leafing through the red OSG and for no reason started to read chapter 5, isolation and switching. At point ii for every other circuit it says blah blah blah......... The device must switch all live conductors in a TT system and all line conductors in a TN system.
The latter point I have no problem with. It's the former. Does this mean ( you should read the full paragraph to be honest. I couldn't be bothered to type it!) that in a TT system all circuit breakers should be double pole? It certainly reads that way in my eyes.
I rarely have any dealings with TT systems, so I don't get involved. But one day I may need to know the answer to this. Anyone?
Simon
 
No. It doesnt say that. Thats what I always thought. Ok, I'm gonna type out the whole bloody thing.
ii Other than at the origin of the installation, every circuit or groups of circuits that may have to be isolated without interrupting the supply to other circuits should be provided with it's own isolating device. This device must switch all live conductors in a TT system and all line conductors in a TN system.

See what I mean?
 
every circuit or groups of circuits that may have to be isolated without interrupting the supply to other circuits should be provided with it's own isolating device.

Do any circuits need to have the facility to isolate without isolating other circuits though?
 
Risteard. Sorry mate but Ive already typed this once before and I don't know where it went! But as I tried to say (puff!) Yes. According to the wording of the paragraph. It also cross references Regulation 537.2.1.1. Whatever that may be
 
interesting... looking at page 34 of the 16th ED. OSG, ( amended 2004 ) the same paragraph reads " all live conductors in a TT system and all phase conductors in a TN system. confusing, huh. all depends on your definition of live conductor.

it would appear to suggest that for TT systems, double pole MCBs are required.
 
Last edited:
Haven't the book on me to lookup that Reg but the point I was making is that perhaps it is not necessary for you to be able to isolate a circuit separately from the other circuits and therefore it does not apply.
 
all depends on your definition of live conductor.

Not really. BS 7671 has always declared that the neutral conductor is a live conductor as it is intended to carry current. It states that, by convention, a PEN conductor is not considered a live conductor however.
 
I think the theme of Risteards reply gives reason why single pole mcbs are ok
The circuits can be isolated at the main switch and need not rely on individual mcbs as isolators
 
No. It doesnt say that. Thats what I always thought. Ok, I'm gonna type out the whole bloody thing.
ii Other than at the origin of the installation, every circuit or groups of circuits that may have to be isolated without interrupting the supply to other circuits should be provided with it's own isolating device. This device must switch all live conductors in a TT system and all line conductors in a TN system.

See what I mean?

See what contradicts in this sentence is "circuits and groups of circuits...without interrupting other circuits" so a group of circuits could be classed as your CU circuits another round in circles regulation.....
 
"Other than at the origin" would mean to me to be, elsewhere double pole would be required,perhaps a remote distribution board

The mcbs are not isolators,if they were to be considered as isolators then yes they would have to be double pole,but they are not,the isolation is the main switch
 
My understanding is that all TN systems have, at some point, a grounded neutral; In TT systems the earth is separated by the use of a completely separate earth path, this may cause the Neutral to rise beyond the approximate 0V which would have been created by a TN system and hence becomes a true live conductor if not isolated.
 

Reply to OSG. Page 33. Is this right? in the Australia area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
346
I have just been called out to another burning shower switch.Upon removal the wires had been burnt and chared.One thing I've noticed on all burnt...
Replies
27
Views
1K
Hi all, I'm planning on adding some lighting to an old stone shed, there's currently a 2.5mm² SWA supply to the shed only supplying one IP rated...
Replies
7
Views
1K
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
827
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
494

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock