Discuss Am i wrongly calculating my maximum demand? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I
iwantmyNVQ
Hi guys i calculating my expected maximum demand for an installation to see if the 60A cut out will handle it.
heres what will go in and calculations incl diversity
2X 32A Rings, so 32A(first ring) + 12.8A (40% all others)
1X 6A lighting, so 4A (66%)
1X10A lighting, so 7A
1X32A Shower, so 32A
1X45A cooker, 10A+ 40%of 35A= 24A
1X32A Under floor heating, 32A
so this equals 144A????
am i missing something this isnt right!!
Ive always taken the biggest mcb away, then add the others togehter, then divide them by 4, then add back the biggest one. Which is about 81A but I doubt you will get anywere near this as it is unlikly you will have everything on all at once.
Jay
so if i do that it comes to 81A, but ive only got a 60A cut out! what can i do client wants to do away with gas heating and oven so everythings going electric!
Its very unlikley you will have everything on all at once. So IMO the 60A should be ok. But if hes adding more stuff then this will need recalculating and maybe then the cut out will need upgrading.
Jay
thanks for the advice jay, its in a block of flats and the suppliers armoured looks about 10mm so is upgrading the cut out an option, surely 80/100 A would require a 25mm, considering its a good 80M run.....
no its a TNS morph...
i understand scientifically that load wont be reached but what happens when it comes to writing out the certs and my demand is higher than the cut out>?:crazy:
When I first started doing testing for a company a few years ago, I asked what should I put in the max demand if it calculated over the cut out rating and they said put half the cut out rating. But now, if its more I just put the acctual size of the cut out because in theory the installation cant demand more that the cut out anyway. A standard 2/3 bedroom house will pull roughly 45A max.
Jay
hi
if tns you could get a 100 A put in , however i would just jot done 60A as max demand they wont say owt, its all a bit finger in the air really anyway to be honest
i have all leccy and a 6o A main fuse and all is cool
yeah that makes sense obv the max USED demand cant be higher than the cut out as itl blow but from the assesors point of view he will notice my design current is higher than my supply will allow so im worried about being pulled up on it. would an explanation that even though there are two rings for functionality of the computer room niether of the rings will be pulling anywhere near 10A!!
thanks jay this is reassuring and well needed meeting with the client tomorrow to tell them if we can go electric UFH or wether we will have to go for a wet system
I was pulled up on my NIC inspection for putting 60 Amps, i said yes i know with gas central heating, no shower and gas hob it probably should be near 40 Amps.
No he replied, because i had put in a lot of circuits he worked it out for me. The answer 160 Amps!!!!!
I just tell them the method i use to work it out now is common sense! Doesn't always go down well though.
I think the underfloor heating should be ok. I dont think your assessor will have a problem with it. To be on the safe side you coud ring the DNO and tell them what circuits you have and what circuits you will be adding and see what they say. But if they need to upgrade the main cut out it may cost you loads.
Good luck with the assessment
Jay
As TC says, the assesor could be a burke.
so he was telling you to put 160A thats ridiculous!!
pahaha sounds about right!!
so can i take the understanding that even tho through applying diversity and the relevant calculations my design current can be higher than the cut out as the likelyhood of it reaching that load is slim?
technically no because design current is what you will really draw,
diversity is different in real terms , also i think its 30 % of full load not 40 % as you mentioned earlier
just put 60 A i would be amazed if the assessor says anything, dont stress it out
Your customer will rue the day they went all electric, ...unless of course they have plenty of money in the old tommy tank!! lol!! ...And totally buggered, if and when they have power cuts for any length of time!!
This is how I would work it out:
1X 32A ring, - 32A
1x 32A ring - 32A x 0.4 = 12.8A
1X 6A lighting, - 6A x 0.66 = 3.96A
1X10A lighting, - 10A x 0.66 = 6.6A
1X32A shower, - 32A
1X45A cooker, - 10A + (35A x 0.3) = 20.5A (It's 30% of what is left over after the 10A (plus socket if applicable), not 40%)
1X32A underfloor heating, - 32A
Then leave out the largest load (in this case one of the 32A circuits where diversity was not allowed), while you work out 40% of what is left, then add together to get a figure:
(This is the part you were missing out)
(32A + 32A + 20.5A + 12.8A + 6.6A + 3.96A x 0.4) + 32A =
75.144A
Then add up all circuits pre-diversity and work out 40% of that total:
45A + 32A + 32A + 32A + 32A + 10A + 6A x 0.4 = 75.6
Providing there is no difference greater than 5A between those two numbers, you can take whichever is the lowest of those numbers to be your maximum demand, otherwise, take the highest. In this case, your maximum demand is 75.144A
This is how I was taught in college anyway.
Seems to me you'll need to shove an 80A in to replace the existing 60A. But don't worry about upgrading the 16mm tails to 25mm ones as 16mm tails are rated at 87A anyway, so you'll be fine there.
Hope that helps :)
If you're doing a re-wire why don't you fit fewer circuits and then the "old" diversity calculation will probably work.
But seriously as more and more homes are getting 8 or 10 way boards the approach to calculating loads needs to be revised.
Personally I add up all the breakers and multiply by 0.4!
Agree here totally with Murdochs thoughts on how the traditional methods (whichever one you use) are increasingly misleading with more circuits on wider boards. A method I'm starting to use more and more is the principal of starting with your max incoming capacity (20kW, say) and then 'spending it' around the install. You almost always have lots of spare to save.
also bear in mind that a 60A BS1361 fuse will run all day up to 100A without blowing.
agreed, but such currents would only be short duration.
Reply to Am i wrongly calculating my maximum demand? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Hi all, 2nd year apprentice. I'm looking to take a supply out to my garage, which is detached, from the DB at the front of the house (2 bed...
4K
Hey guys I really need urgent help understanding this Basically I'm trying to calculate what the diversity factor/percentages would be for the...
5K
I'm always in a dilemma with regards max demand. Often you work it out and it's higher than the the 80A or 60A cut out fuse. However, you know...
This isn't sitting right with me. So if I rock up at a house with a 60A suppliers fuse, it has a dear old Wylex with 1 RFC 30A (no diversity) 1...