Discuss Is this a C2 or C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Is that standard electrical tape? or self-amalgamating tape?

Assuming that the sheath has been removed beneath it, then it is not suitable as replacement insulation (despite the name), so the issue would be basic insulation visible outside of enclosure, which is usually a C2.

However, if this was up in the ceiling, and there were no metal parts that it might touch, I might well consider this a C3, as it's not accessible to touch...

Pretty much every new build in the last 20 years probably has this in every downlight though (usually without the tape).... unless they've since been replaced by someone with the time to do things properly....
 
The tape makes no difference it is not suitably enclosed.
Agreed - though if it was self amalgamating tape (that couldn't be removed without a tool), that would make things slightly different would it not? Looks more like tape I agree....
 
From BPG4:

(C2) Sheath of an insulated and sheathed nonarmoured cable not taken inside the enclosure of an accessory, such as at a socket-outlet or lighting switch, where the unsheathed cores are accessible to touch and/or likely to come into contact with metalwork. (Note: Code C3 would apply if the unsheathed cores are not accessible to touch nor likely to come into contact with metalwork)
 
Typical builders installation job, i guess atleast they joined the earths and didn’t just cut them off like 99.9999% of builders normally do

inspectors hat on C2

real work hat on C3 as it’s up in the ceiling void and under normal circumstances unlikely to ever be touched by anyone
 
From BPG4:

(C2) Sheath of an insulated and sheathed nonarmoured cable not taken inside the enclosure of an accessory, such as at a socket-outlet or lighting switch, where the unsheathed cores are accessible to touch and/or likely to come into contact with metalwork. (Note: Code C3 would apply if the unsheathed cores are not accessible to touch nor likely to come into contact with metalwork)
so that makes it a C2 as shown in the OP's pic., but a C3 when shoved back in the ceiling? push it back up andvcharge £100 for remedial work.
 
so that makes it a C2 as shown in the OP's pic., but a C3 when shoved back in the ceiling?
Guess so! Though there is the argument that if the downlight itself is metal (and not earthed), then maybe it should be a C2 if either of the live conductors could touch it....

There is also this:

Unenclosed electrical connections, such as at luminaires. (Such a defect can contribute to a fire, particularly where extra-low voltage filament lamps are used)

Which would mean always a C2 if the terminal blocks were outside the enclosure I guess....

I don't think I've ever seen a new build with downlights that aren't like this picture (minus the tape) though
 
Not sure if it’s the same model of fitting, but the little black jointbox should be clipped to the metal plate sticking out to the left. This plate may also have a threaded hole that should take an earth terminal screw.

So by design, the fitting should have been earthed.... but isn’t. C2

Other fittings may be double insulated (look for a square within a square logo)
If so, then C3, basic insulation outside enclosure.
 
Isn’t basic insulation outside of the box a C2 , potentially dangerous as their is not mechanical protection on the single cables
 
Give me a break, have you seen the time?

yes.... it’s also a C2. Unwrap the tape and see how much basic insulation is showing.
I wouldn’t spend 2 mins trying to peel off the tape, just Cut off builders tape bodge job, reterminate both twin n earth into a choc box and take 6 inches of flex to light fitting and connect properly

(yes it’s early :)
 
The guy that did my EICR report said he was an EICR inspector who also trained other inspectors. He said he was going to class it as a C2 as the cables should have been enclosed in a coffin box, he never mentioned anything about the earthing
 

Reply to Is this a C2 or C3 in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
612
See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
307
A pull-cord shower switch is located in Zone 2 of a bathroom, including the ceiling base containing the electrical connections. With a little...
Replies
6
Views
736
EICR picked up no continuity on cpc on 3 pendants fittings in a grd Floor Flat. Zs measured @ other pendants & complies. Different opinions on the...
Replies
8
Views
419
How would you personally Code a Tubular Heater that was fixed to a Wall Horizontally with Two brackets. The Heater being about a meter long but...
Replies
6
Views
659

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock