Discuss 18kw heater - 45m cable run - 3 phase - rewireable fuses. . . . Fuse size ???? in the UK Electrical Forum area at ElectriciansForums.net
E
Eric-George
Hi Guys,
Firstly, this is my own project and I have no 3ph supply in my own unit and have to take a supply from neighbors unit who has an old 3ph rewireable board with plenty of spare spaces.
I cant upgrade neighbors board and have to run a cable 35- 45m to supply a 18kw heater and fans.
My question is what size fuses do I need ??
The total current works out to be 43 amps with a 3.3% volt drop.
This gives me a minimum cable size of 6mm 4 core swa.
The question is . . . . . Do I try to source 45a fuse wire to cover the total current load or is the total current (43a) divided by the 3 phases making the fuse sizes smaller ???
Appreciate all your suggestions.
is the heater and fans single phase or 3 phase?
Not sure where you got that 43amps from as an 18kw load over 3 phase would be 26amps per phase
Malcolm, you may have just answered my question. I got the 43a from dividing power by voltage (18000 / 410). I'm sure there a square root of 3in the calculation that I've missed?
43/ sqrt 3 (1.73) = 26 !!
Telectrix - Fans and heater are all 1 unit with 3 ph supply.
think the way forward is to split the tails to the neighbour's DB, install a 40A 3 phase MCB to feed your installation, add a meter if required so neighbour can charge for what you use. 6mm SWA if it meets VD limits beats 3 rusty nails in his DB.
Reply to 18kw heater - 45m cable run - 3 phase - rewireable fuses. . . . Fuse size ???? in the UK Electrical Forum area at ElectriciansForums.net
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
Hi all, Hope you're keeping well I'm currently wiring a small commercial premises. 3 phas incoming supply, 16sq cables As it is in an urban...
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...