DNO came round today to check voltage after customer complaint about very high mains voltage over 250vac. First thing engineer asked "have you got solar panels installed?". He said this is a common "fault" and request from customers with solar PV. Its now turned down to 240VAC on the pole (still not the 230vac, if we will ever see that rolled out?) lol
 
I have had thius problem, apparently some of these inverters were meant for other coutries and they do not conform to our regs. Try taking the black cover off and underneath you will see there are three wheels with numbers on, set the one on the left five and the one next to it to eight. This will set the inverter to our G83 setting, do not mess with grid guard code that is a bit tricky, I have set three inverters like this and they all worked fine afterwards.
 
I have had thius problem, apparently some of these inverters were meant for other coutries and they do not conform to our regs. Try taking the black cover off and underneath you will see there are three wheels with numbers on, set the one on the left five and the one next to it to eight. This will set the inverter to our G83 setting, do not mess with grid guard code that is a bit tricky, I have set three inverters like this and they all worked fine afterwards.

Blimey if you didn't do that during commissioning.......... The SMAs will lock after a few hours running and WILL require the grid guard code.

Anyway I spoke to G59 commissioning witness guy the other day and he has been to numerous jobs where the installer didn't understand that the inverter settings needed to be ukg83/g59 and they weren't even able to show what it was set to, some right muppets out there....
I have to say don't touch what you don't understand !!!!
 
  • Like
Reactions: 1 person
I have never had one lock and I have fitted about forty of these inverters, they do not normally need setting they should come factory set to G83, this is what I was told to do by SMA.
Blimey if you didn't do that during commissioning.......... The SMAs will lock after a few hours running and WILL require the grid guard code.

Anyway I spoke to G59 commissioning witness guy the other day and he has been to numerous jobs where the installer didn't understand that the inverter settings needed to be ukg83/g59 and they weren't even able to show what it was set to, some right muppets out there....
I have to say don't touch what you don't understand !!!!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
2 SB 3800 Inverters, 9600 kwp array, one 60m export cable. Inverter cutting out?
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
Blueflash,
Last reply from
Running Pob,
Replies
23
Views
3,731

Advert