Hi folks.

I cut one of the cables on my ring circuit, attached the 2 now separate ends to a new 30a junction box, and then run 2 additional spurs from the same junction box, using 32a twin and earth, on the end of each of these new spurs is a twin plug socket with usb.

I did the work with my father in law, who’s an avid DIYer and has been doing diy for 60 years.

We did a really good job, cables cut nice, neat, secure, tested them, and all working.

Due to a rush to get the job done before decorators, I pre installed the new sockets and cabling, ready for the junction, and only then did I realise I should have extended the ring.....it was too late, I had sealed the walls up and could not get another cable in. We used a square 30a MK box, which had ample room for the cables.

These are bedside outlets, not for heavy consuming items.

Some forums and people have now put the fear of god in me that this is dangerous, however I have read mixed opinions (e.g. apparatly 1 spur from any point is the Reg, ok.....so I have 2 on mine, but is this really much different than if I added another junction 10 inches away for my second spur)

Is this really a concern to warrant me ripping it all back out?

It’s a good tidy job.
I know there’s regulations and partP......hindsight is a wonderful thing.

Views?
Many thanks.

452805D2-13E6-4F2C-A5C7-A949BBC783E1.jpeg
 
OP. Basically fella, you’ve opened a can of worms.

After reading this, and seeing SparkyChick taking on the forum. My opinion is: What you’ve done is bad practice and I would never ever do it like this, and I’ve always been taught that this is wrong. But - hey, it doesn’t appear to be against regs when you scratch beneath the surface.

Talk about a grey area.
 
I've searched and I can't find any reg that proves this againt regulation, thats not to say it doesn't exist.

Personally in this situation and working with what you have, overloading would be my main concern. You could always fuse each of the sockets to a more suitably reduced fuse and/or label the sockets for specific use only.
 
This is almost as good as getting a phone call from a spark who was spitting feathers about the fact that I'd put a 2.5mm radial on a 32a mcb and made it '2 circuits' when all I'd done is take a spur from the MCB!
Think about the Physics for a second...would a 2nd jb and a few inches of cable materially alter the way the circuit operates? No...so why do it?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Wales

Thread Information

Title
2 spurs from a Junction Box....worried?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
237
Unsolved
--

Advert

Thread statistics

Created
mikep83,
Last reply from
SparkyChick,
Replies
237
Views
40,856

Advert

Back
Top