E

EastAnglian

My mate & I were wondering how the pole-mounted "transformer" is configured on a farm where we've been working.

The overhead supply is very clearly just 2 wires mounted on poles across the field. There is a large transformer mounted on the pole and the presentation at the service head is 3 x 100A fuses, all live, (400V between any two) giving the appearance of a 3P+N supply with TT earthing system.

However, only 2 of the fuses are connected to the meter, and are marked L1 and L3 .... which then go on to power the farm and farmhouse.

So we were musing is this really a 3P supply? If so, how is the transformer configured? There appear to be no moving parts on the pole.

Anybody any good at distribution topologies?
 
Hi EA, Like Tony I suspect your measurements are wrong and that there is more likely to be 230V between either Line (L1 or L3) and Earthed Neutral (EN) and 460V between Lines (L1-L3). Both Lines are offset from the Earthed Neutral by half a cycle (180°). This is called a Two Pole, Split Phase Supply, often wrongly called 2 phase or bi-phase. It's common for long supply runs in rural areas, supplying isolated farms in particular, as it saves the DNO the cost of supplying a third line conductor.
 
Last edited by a moderator:
Thanks guys - I did suspect it wasn't three phase, and the voltage measurements were done quickly some while ago!

So in this arrangement what is the third incoming (non-connected) service fused cable? It is certainly live.
 

Reply to 2 wire overhead feed to 3 phase installation in the Australia area at ElectriciansForums.net

Similar Threads

Hello. How i should connect this 1 phase 2 pole 400v cooling pump? If i apply 1phase 230v and neutral it Will only growl and "spin" very very...
Replies
11
Views
714
Hi everyone, Quick question can you fit an RCD without any neutral connections? If I have a 3 pole circuit breaker which has all 3 poles...
Replies
16
Views
2K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
920
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
So, the actual job is on a farm. I think I'll keep things simple at the moment and just ask about voltage drop. I'll come on to earthing and...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock