SparkyDips

hello guys i overheard a conversation last week about a supply to an outbuilding which will comprise of: 45A Shower, 32A Ring Final and 6A lighting. Total demand = 83A.

outbuilding is 28Mtrs from main house and will have no extraneous conductive parts as the water feed will be plastic.

now the spark was saying that a 25mm SWA buried in the ground will need to be run and can use the house main earth.

whats your thoughts on this guys??

regards
 
10mm is well adequate. the guy is talking through his arse. has he not heard of diversity?
 
25mm swa seems abit over the top to me. Doing a rough calc, 83A x 0.4 = 33.2A. Do some calcs and you will know what size cable you need.
Although I useally take out the biggest mcb, then add the rest, divide by 4 then add the biggest back for your total. This gives a slightly higher demand but still no need for the 25mm swa.lol
 
sorry, jay. you need to allow 45A for the shower, the 0.4 of the rest. that equates to around 60A.
 
  • Like
Reactions: 1 person
so 10mm having 60A CCC and 16mm having 78A CCC more than adequate.

25mm having 99A CCC lol
 
then again that shower may not pull over 40A . manufacturers are overly optimistic with their figures.
 
yes true. i think i may suggest that 35mm "just to be safe" will be better and cheaper in the long run!! lol
 
I wonder which is the right way of working out demand?? I do the same by taking away the biggest mcb and adding it back to the total but I was tought to divide by 4. I know alot of lads multiply by 0.4. I suppose doing it the multiply by 0.4 way will give you a slightly higher demand and air on the side of caution!!
 
Funny how the question is always asked in the 2[SUP]nd[/SUP] inst. It’s never I think it should be what ever, but my friend thinks it should be……….

Funny old world. Or am I a cynic?
 
  • Like
Reactions: 1 person
No diversity on shower, any specifics what else will be plugged in? Il say 60A on 63A breaker = 25mm
 
a lot of confusion arises over the fact that while a MCB may be 32A for a socket circuit, say, the actual load of the circuit may never get above 20A, sometimes even a lot less if it's not a kitchen RFC.
 
  • Like
Reactions: 1 person
too late for calculations Tony!! Saturday night is beer time! lol

with this sort of attitude its no wonder people are put off making a post!!
 
its not a kitchen, will be a small gym comprising treadmill and rower. with shower.

i have been doing the comms cabling and just overheard this conversation.
 
No diversity on shower, any specifics what else will be plugged in? Il say 60A on 63A breaker = 25mm

you got shares in a copper mine?
 
  • Like
Reactions: 2 people
Yes jay i gather it up on all jobs like a pikey i suppose.. £300 quid will buy the cable
 
We on big site at moment and full of scrap metal, copper boilers the size of a small car. Mmmmm, the plumbers are at it.

I said what's that boiler lying in bushes for, they said the boss is taking it, the boss came back to lift there rubble and they didn't mention it and piled all rubble away from it at bottom of path, crafty buggers.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
25mm SWA!!
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
44

Thread Tags

Tags Tags
25mm swa

Advert

Thread statistics

Created
SparkyDips,
Last reply from
SparkyDips,
Replies
44
Views
4,148

Advert