M
Marvo
I had a request from one of our suppliers who, from time to time, we also assist with their warranty claims. They had an 'electrician' who purchased a 3kW borehole pump and returned it next day as being faulty. The supplier provided a replacement pump and did a post mortem on the returned item in the hope of shedding some light on what the problem might be. They had an idea it was an electrical issue but that was as far as they'd got.
Next day the guy was back again with the second pump claiming he'd taken it to site and tested it in a pond before he installed it down the borehole only to find that it also had a problem and the start relay was chattering. Apparently they begrudgingly gave him a third pump which they tested in the workshop in front of him before he left on his merry way. That afternoon they received a phonecall saying the pump ran for about 15 minutes and it's also now faulty.
They contacted me to go to the site which is about 120Km away and please check the installation for anything that might be causing problems.
Here's a few pictures of the installation;
The supply cable for the borehole pump was plugged into an external socket that was mounted on a large concrete water holding tank. The socket had been installed directly off an existing 2.5mm supply that was for a level control and alarm that is in turn run from an outbuilding 130 meters away. The outbuilding is supplied on a 2.5mm SWA from a residence that was another 50 meters away from the outbuilding.
From the socket shown above the cable was run through the bush and undergrowth for approx 180 meters to the borehole control box which contains the overload and and start relay.
The control box then supplies the pump which is another 10 meters away across the surface then 160 meters down in the bore hole.
I noticed a couple of quality touches such as the warning cone which I thought was ironically suitable and the last 5 meters before the borehole was into conduit.
I was kinda curious if he'd used conduit inside the hole or whether his unsupported flat twin was sufficient on its own for the descent but I was itching to get back out of there before I bumped into him in case he wanted to discuss the finer points of the installation with a fellow professional.
I delivered the shortest report I think I've ever written and gave them a couple of dozen photos. For some strange reason they've declined to give him a fourth pump under warranty.
Next day the guy was back again with the second pump claiming he'd taken it to site and tested it in a pond before he installed it down the borehole only to find that it also had a problem and the start relay was chattering. Apparently they begrudgingly gave him a third pump which they tested in the workshop in front of him before he left on his merry way. That afternoon they received a phonecall saying the pump ran for about 15 minutes and it's also now faulty.
They contacted me to go to the site which is about 120Km away and please check the installation for anything that might be causing problems.
Here's a few pictures of the installation;




I was kinda curious if he'd used conduit inside the hole or whether his unsupported flat twin was sufficient on its own for the descent but I was itching to get back out of there before I bumped into him in case he wanted to discuss the finer points of the installation with a fellow professional.
I delivered the shortest report I think I've ever written and gave them a couple of dozen photos. For some strange reason they've declined to give him a fourth pump under warranty.