Discuss 7.6kW Induction Hob - need to select cable and fuse size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Because the existing useable feed is a 6mm from a 32A RCBO so would be easiest to use the cable and possibly feed hob & Oven, would've thought it would be frowned upon to use anything smaller through a cooker switch which is 45A and therefore large terminals. Suppose could run out a 2.5 T&E from the cooker switch but.
 
Because the existing useable feed is a 6mm from a 32A RCBO so would be easiest to use the cable and possibly feed hob & Oven, would've thought it would be frowned upon to use anything smaller through a cooker switch which is 45A and therefore large terminals. Suppose could run out a 2.5 T&E from the cooker switch but.

Wtf? You are talking about running a new circuit from the CU in 6mm and fitting a 45A switch for a 4KW load?
Do you run all 16A radials in 6mm?
 
No of course not 6mm on 16A radials !
I think my point is being lost, right now there is a 6mm fed in, it was jointed in a jb and split to feed old hob & oven, I would like to feed new hob & oven with it and just locate the cooker switch to a position within regs. I had no idea if being induction hob would need full load rated to be calc and no diversity and as oven is seperate and singular there would not be diversity on it due to my understanding it's one element and so can't be diverse. It's themostatically on or off. So I was wondering if I need a new seperate radial run in for oven, and as Lee said I would rather go to 4-6mm if needed to cover any future larger load being fitted e.g. Customer decides they fancy a double oven later to cope with family and for instance 11kW.
 
No of course not 6mm on 16A radials !
I think my point is being lost, right now there is a 6mm fed in, it was jointed in a jb and split to feed old hob & oven, I would like to feed new hob & oven with it and just locate the cooker switch to a position within regs. I had no idea if being induction hob would need full load rated to be calc and no diversity and as oven is seperate and singular there would not be diversity on it due to my understanding it's one element and so can't be diverse. It's themostatically on or off. So I was wondering if I need a new seperate radial run in for oven, and as Lee said I would rather go to 4-6mm if needed to cover any future larger load being fitted e.g. Customer decides they fancy a double oven later to cope with family and for instance 11kW.

I think Richard has covered it well in #29. Locate the cooker switch in a convenient/correct location and fit a dual connection plate for hob and cooker.
 

Attachments

  • image.jpg
    19.2 KB · Views: 35
Wtf? You are talking about running a new circuit from the CU in 6mm and fitting a 45A switch for a 4KW load?
Do you run all 16A radials in 6mm?[/QUOTE
If it was a new supply for an oven in lets say a kitchen extension to a property, then yes I would run it in 6mm with a 32A breaker on a 45A DP switch and socket. Best start using the push bike to get to work, will save the customer a few quid. FFS.
 

Reply to 7.6kW Induction Hob - need to select cable and fuse size in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
523
Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Hi all I'm in the process of swapping out my 4 zone CDA induction hob for a 5 zone Bosch. Currently the existing wire starts as a 5 core cable...
Replies
10
Views
2K
The electrician that installed my cooker circuit put in 10mm cable with a 32a fuse, a 45a cooker switch and 10mm cable to the backplate for behind...
Replies
23
Views
1K
Hi all, I’m now ready to install my hob, I have a 32A MCB with 6mm T&E feeding a 50A rated switched supply at the worktop. The hob isn’t supplied...
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock