just done my first private job which included a new lighting circuit, new radial, and extending a ring, in a workshop/ car port. the board had been installed new 6 months ago and had no rcd on any circuits so i put an rcd covering all circuits. do i now have to re test every circuit for the certificate or can i just do the ones i altered or added? also i had problems doing an rcd test which turned out to be a 100 ma rcd on a circuit which was powering a stable which is fed from a 40a type b breaker at the workshop board. the 100 ma was faulty so i just connected straight through as its covered by the 30ma i just installed. after this the rcd test was ok untill all circuits were on then the auto test would not run through, but each circuit would test out fine individually, i have a 40,32,32,16,6,6a breakers on one 63a rcd but theres not much load on any circuits? any advice is appreciated, thanks matt
 
Do you think the RCD upfront may have been a bad idea. Did all the circuits need to be RCD protected?? when you say the "auto test would not run through" what did you mean ? would it trip or not trip
 
not sure, why do you think? theres 2 ring mains, 1 radial, so all skts. a 10mm t&e to a box then conected to an armored cable feeding a stable, and the lighting which doesnt need to be but i thought why not put them on if the circuits test ok. my tester has an auto test which runs through 8 tests, its a metrel combi. it basically wont run through the whole cycle with all circuits turned on but if you switch some off it will, but its not a problem with any specific circuit, do you think i should take the lighting off the rcd, the 10mm t&e to stable has skts so doesnt that need to be on an rcd?
 
not sure, why do you think? theres 2 ring mains, 1 radial, so all skts. a 10mm t&e to a box then conected to an armored cable feeding a stable, and the lighting which doesnt need to be but i thought why not put them on if the circuits test ok. my tester has an auto test which runs through 8 tests, its a metrel combi. it basically wont run through the whole cycle with all circuits turned on but if you switch some off it will, but its not a problem with any specific circuit, do you think i should take the lighting off the rcd, the 10mm t&e to stable has skts so doesnt that need to be on an rcd?

urchy107 its really hard to tell without seeing it / more specific information.

I'm sure the problem may very well be with a specific circuit ... ?

Have you done any dead tests? Checked for electrical separation, IR on each circuit. You'll be amazed what you can find. recently dismantled a sub main SWA that was working, 20 Metre run buried 2 inches under a lawn with the mother of all botched joins in the middle (full of chewing gum , no R391 left I guess). IR was 230,000 Ohms between each conductor (or thereabouts). But it worked.
 
Last edited by a moderator:
Why are you testing the circuits individually with the rcd tester
If you have verified its working correctly at source,then circuit loads or faults could give you incorrect information
The Rcd tests are the correct function, or not, of the Rcd
 
ok, im aware that you only need to test the rcd once on one circuit but i was thinking that if it wont test properly with all circuits on then it may not function properly in normal conditions if there was a fault?
 
ok so i have no problem then. sweet! but i have never had to isolate circuits before to do the auto test and the way i looked at it was that in the real world all cicuits will be on, have you had to do this before to get a reading then?
 
The range of tests carried out for an installation will each serve to verify if its within stated limits for each type of test
An insulation resistance test can have a false result if there are items in circuit to affect the test
A test for Ze can be affected if there are parallel paths
An Rcd test can give false readings if there are loads or low neutral/ earth insulation readings

Each test supplements the others and the result is the combination of all tests carried out as per guidances,rcd tests at the source will show whether its ok or no
Rcd tests using a circuit will or could be affected by the circuit itself
 

Reply to adding rcd to board wont test in the Australia area at ElectriciansForums.net

Similar Threads

I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
875
I live in Australia; you can use a socket tester to test the RCD for the power outlet circuit. Plug device to a 3-pin wall socket, set testing mA...
Replies
2
Views
879
Hello, I am in the process of training to be an electrician and have a question. When filling out a EIC for a new circuit am I required to test...
Replies
2
Views
1K
Hi, while testing the new board I installed I got to the live testing at the sockets one of the RCD's kept tripping during the loop test, the...
Replies
4
Views
1K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock